for 12KW motor which cable size has to select for ex.10
meter.
Answers were Sorted based on User's Feedback
Answer / prodip das
1. we have to select cable
for that first calculate current=12X1000/1.73x400x.95
=19 Amps
Type of cables= single core NYY(Red/Yellow/Blue/Green)
Cable size3x1CNYY
NYY 2.5 sq.mm
(ccc)=19.61A
Group rating=.68
sand bed=.90
Rating factor=.68x.90=.61
Actual CCC OF 2.5SQ.MM CABLE
=19.6X.61=11.96A
=26.20x.61=15.98
=33.63x.61=20.5143(OK)6 sq.mm
Votlage drop as per IEE regulation
Distance=10m(more)
=5.9x10x.152=8.968V(ok)
Finally SWG=6sq.mm
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / abdulsubur
FROM THE FORMULA P=ROOT3 VICOS PHI
12/ROOT3*400*.85 WE GET I=20
VD= MV*L*I/1000
WE GET 10 SQR MM+EARTH CABLE 6 SQR MM
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / phanendra babu
the selected cable should have the capability of
withstanding the over load /short ckt currents upto before
operating the protecting device. so assume 0.81 p.f,the load
current is given by apprx 20A .very safe working of copper
cable is 4A to 6A per 1sqmm ,so the size of the cable
suitable for 12kw motor is 6sqmm. copper cable or 16 sqmm
aluminum cable.
the above calculation is for lo current ratings if current
rating increases capacity will decrease.
Is This Answer Correct ? | 4 Yes | 1 No |
The cable size will depend on the you rated voltage and
cable route you can reffered to
IEC 60364-5-52 Electrical installations of buildings -
Selection and erection of electrical equipment - Wiring
systems
or from electrical installation guid from schneider site.
Is This Answer Correct ? | 5 Yes | 4 No |
why the earth pin in a 3-pin socket is longer and thickest?
when we switch on the switch and load is not connected at home,is electricity wasted?
what is a universal motor? how it works?
what is the difference between the voltage of 5 volts capacitor and and 5volts battery?
what is SWA type of cable?????
what are the losses of capacitor??
please explain to me how to calculate current,voltage,resistance with formula??
How can remove the jerks on genretor due to remov or connecting the load ?
why a fan starts rotating in the reverse direction when condenser gets damaged?
Why electrical engineer use Cu Strip for transformer neutral why not GI Strip? What if we use GI instead of Cu does it affects the transformer performance.
How can we measure earthing resistance test (Earth meggar) of Transformer neutral pit while in live condition?.
How to identify the start and end of 3phase 12 lead motor if U1, U2, etc numberings are lost or erased.