for 12KW motor which cable size has to select for ex.10
meter.
Answers were Sorted based on User's Feedback
Answer / prodip das
1. we have to select cable
for that first calculate current=12X1000/1.73x400x.95
=19 Amps
Type of cables= single core NYY(Red/Yellow/Blue/Green)
Cable size3x1CNYY
NYY 2.5 sq.mm
(ccc)=19.61A
Group rating=.68
sand bed=.90
Rating factor=.68x.90=.61
Actual CCC OF 2.5SQ.MM CABLE
=19.6X.61=11.96A
=26.20x.61=15.98
=33.63x.61=20.5143(OK)6 sq.mm
Votlage drop as per IEE regulation
Distance=10m(more)
=5.9x10x.152=8.968V(ok)
Finally SWG=6sq.mm
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / abdulsubur
FROM THE FORMULA P=ROOT3 VICOS PHI
12/ROOT3*400*.85 WE GET I=20
VD= MV*L*I/1000
WE GET 10 SQR MM+EARTH CABLE 6 SQR MM
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / phanendra babu
the selected cable should have the capability of
withstanding the over load /short ckt currents upto before
operating the protecting device. so assume 0.81 p.f,the load
current is given by apprx 20A .very safe working of copper
cable is 4A to 6A per 1sqmm ,so the size of the cable
suitable for 12kw motor is 6sqmm. copper cable or 16 sqmm
aluminum cable.
the above calculation is for lo current ratings if current
rating increases capacity will decrease.
| Is This Answer Correct ? | 4 Yes | 1 No |
The cable size will depend on the you rated voltage and
cable route you can reffered to
IEC 60364-5-52 Electrical installations of buildings -
Selection and erection of electrical equipment - Wiring
systems
or from electrical installation guid from schneider site.
| Is This Answer Correct ? | 5 Yes | 4 No |
Write a note on materials used as a fuse element.
explain why tap changer is always connected to high voltage winding side of the transformer.
what is the generating transformer?
how we calculate fault current& load factor or fault level&also the leakage current
WHY EXCITER PHASE SEQUENCE ARE OPPOSITE THAN STATOR SUPPLY PHASE SEQUENCE IN SYNCHRONOUS MOTOR >
what is the star delta connetion and how can do it a three phase motor with control witing with picture
0 Answers Aurobindo, SA Kent, Wipro,
How can we explain that what is the power factor?
why holding contact is not using in VCB and ACB breakers?
why do we generate only 3ph ac?is it possible to generate 4ph,5ph,....?
6 Answers Accenture, Bhel, Reliance,
wat is the difference between BE &BTECH.
you have an automatic voltage regulator at home for your appliances,if the voltage in your area drops from 220v to 190v,does the output of the automatic voltage regulator drops?or does it retains the 220v output?
how do we connect mcb in our home?and how does it work?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)