Answer / prodip das
1. we have to select cable
for that first calculate current=12X1000/1.73x400x.95
=19 Amps
Type of cables= single core NYY(Red/Yellow/Blue/Green)
Cable size3x1CNYY
NYY 2.5 sq.mm
(ccc)=19.61A
Group rating=.68
sand bed=.90
Rating factor=.68x.90=.61
Actual CCC OF 2.5SQ.MM CABLE
=19.6X.61=11.96A
=26.20x.61=15.98
=33.63x.61=20.5143(OK)6 sq.mm
Votlage drop as per IEE regulation
Distance=10m(more)
=5.9x10x.152=8.968V(ok)
Finally SWG=6sq.mm
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / abdulsubur
FROM THE FORMULA P=ROOT3 VICOS PHI
12/ROOT3*400*.85 WE GET I=20
VD= MV*L*I/1000
WE GET 10 SQR MM+EARTH CABLE 6 SQR MM
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / phanendra babu
the selected cable should have the capability of
withstanding the over load /short ckt currents upto before
operating the protecting device. so assume 0.81 p.f,the load
current is given by apprx 20A .very safe working of copper
cable is 4A to 6A per 1sqmm ,so the size of the cable
suitable for 12kw motor is 6sqmm. copper cable or 16 sqmm
aluminum cable.
the above calculation is for lo current ratings if current
rating increases capacity will decrease.
| Is This Answer Correct ? | 4 Yes | 1 No |
The cable size will depend on the you rated voltage and
cable route you can reffered to
IEC 60364-5-52 Electrical installations of buildings -
Selection and erection of electrical equipment - Wiring
systems
or from electrical installation guid from schneider site.
| Is This Answer Correct ? | 5 Yes | 4 No |
Explain the role of a car driver as one of a feedback mechanism.
How to calculate % Impedence?
why should a transformer be never connected to dc supply
c. int m = 10; main() { int m = 20; {int m = 30;} printf("%d %d",m,::m); 1. 10 10 2. 10 20 3. 20 10 4. 20 30 5. 30 20 6. None
What is the general power consumption rating of CPU CRT type and Flat type, Monitor,Printer, projector, Scanner?
if transformer winding burn on dc supply then why not alternator rotor winding please post answer on y.sakhare@rediffmail.com
I If i have 2kv ups in which 38Amp *8battries hou many hour's back up i get from 600Watts
what would happen if reactive power (kvar)is increased (more)or decreased (less)? how much exact reactive power should be maintained? and what should be done for that
what will happen if instead of neutral we use earth wire as return conductor?if we can use ,then why we are not using in our day to day appliances?please justify the answer
WHAT IS THE TOTAL POWER GENERATION IN CHHATTISGARH?
Ht panal kia hota ha?
internally connection of photvoltic module
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)