How Negative Phase Sequence Relay works in case of
Synchronous Motor?
Answers were Sorted based on User's Feedback
Answer / deepak patidar
When the load on the generator becomes unbalanced, negative
phase sequence currents flows. The negative sequence
components produce a rotating magnetic field which rotates
at synchronous speed in a direction opposite to the
direction of rotor field. Hence effectively the relative
speed between the two is double the synchronous speed. Thus
double frequency currents are induced in the rotor. These
currents cause sever heating of the rotor and can cause
damage to the rotor. The unbalanced stator currents also
cause sever vibration and heating of stator. Hence it is
necessary to provide the negative sequence protection to
the generators against the unbalanced load condition.
The negative phase sequence filter alongwith the
overcurrent relay provides the necessary protection against
the unbalanced loads.
| Is This Answer Correct ? | 25 Yes | 3 No |
Answer / alee xain
We use a negative sequence filter to filter out negative
sequence component, its characteristics are similar to that
of Inverse overcurrent or over voltage relay. we operate
such a relay on the basis of these negative sequence
component of fault current.
| Is This Answer Correct ? | 13 Yes | 15 No |
Answer / j.venkatesan
In case of the numeric relay the negative phase sequence
current is calculated bu NPS=Ir+a2Iy+aIb.
Where a is an 120 degree phase shift opeator.
This calculated NPS is used for operation of the relay.
| Is This Answer Correct ? | 3 Yes | 7 No |
Answer / 32r
deeepak patidar the questin is regarding syn. motor so pls make it clear
| Is This Answer Correct ? | 0 Yes | 4 No |
why EMF IS INDUCED IN A CONDUCTOR WHEN FLUX LINKING WITH IT CHANGES ACCORDING TO FARADAYS LAW.
how to calculate the size of cable tray
how hydrogen or helium is a cooling agent for alternator./ generator of big size.
If load is 240 kw & pf is 0.8 lagging, than how to increase it from0.8 to 1.0(unit),which rating capacitor used, please give me Calculation. What is effact of consumer & suplier if pf is lagging or leading with on effect machines/ TF/GE etc.
help!!!! i bought a new house 2 yrs ago,ive just had 2 new lights fitted,when i boil the kettle,maybe 2 times in succession the safety light switch trips out,it dosnt do it straight away but it seems to do it when the kettle boils!!!!! sounds very odd to me
an off load but energized 11/0.4 KV, 1250 KVA T/F has a power factor of 0.65(capacitive)..!! why is it so, though T/F being an inductive device ??
How to Calculate Current Rating of SDFU (Switch Disconnector Fuse unit) for Protectionof Capacitor Bank connected to Busbar of 800Amp,in LV side of 11/0.433KV, 250KVA Transformer?
How Negative Phase Sequence Relay works in case of Synchronous Motor?
What information we need to prepare relay coordination chart
what are the names of oil used in transformer and its chemical name?
How can we calculate earth mat conductor size ..? & give the formula to determine earth conductor size?
what is the function of avr when synchronous generator act as synchronous motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)