What will the new flow factor if D/P Transmitter is
RE-RANGED from 25" WC to 50" WC
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Answer:
The flow rate at 50.0"wc will be 141.4% of the flow rate at
25.5"wc.
Reason:
The design maximum flow rate at 25.0" is 100.0% flow rate.
Flow rate is the square root of the percentage of flow at a
given DP.
The flow rate at 25.0"w.c. DP is the square root of 1.00 (or
100%)
If the DP doubles from 25.0 to 50.0, then the DP increases
from 100% at 25.0"wc to 200% at 50.0"wc
The flow rate at 200% DP increases by 141.4% because the
square root of 2.00 (or 200%) is 1.414.
Carl Ellis
Measure First
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / enka group iraq
Ans;- A simple calculation is as follow :- Q1 / Q2 = √DP1/√dp2
Q1= Q2 X √DP1/√dp2
Q1 = new flow factor, Q2 = existing flow factor
DP1 = transmitter new range DP2 = transmitter existing range
Q1 = Q2 X √50/25 = Q2 X 1.41
The new flow factor will be 1.41 times higher then the existing flow factory
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / selva
The ratio of
New factor New range
---------- = -----------
Old factor Old range
| Is This Answer Correct ? | 0 Yes | 2 No |
what is burner management system?
rtd principle?thermocouple principle?
what is working principle of vibration prob
A pressure differential gauge type of instrument has a manifold with 2 isolation valves (hp and lp),2 vents(1 each for hp and lp) and 1 equalizing valve. Determine the position of each valve(either fully closed or fully open) when troboulshooting to: 1. zero the transmitter. 2. determine if there is a block in the impulse line. 3. determine if the gauge is functioning properly. The process fluid is water.
why we are using pnp npn for sensors is there any other type?
ALL INSTRUMENTS WORKING PRINCIPLE.
3 Answers Blanco, India Cements, TVS,
Sir, I am working as a Instrument Engineer in Grasim Industries. Can any body provide question answer for interview purpose
Explain the usage of the PLC system?
what is the full formof HART
What different types of problems do occur while doing the loop checking? and please explain in detail or mail me at kadam.aniket143@gmail.com
1 Answers Operational Energy Group, Process Control Technologies,
generally for transmitter we are giving supply 24vlts?but we are getting output 4-20ma ? how it is possible? is there any operation inside the tx?pls give complete information?
please can anyone tell me in detail, what's mean by open loop and close loop?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)