What is mean A32 B32 C32 D32 in mcb(miniature circuit breaker)
Answers were Sorted based on User's Feedback
Answer / sudipto jena
hello,this is sudipto,from rourkela
In the above question ,there is a alphabet and then two
digits are present in the code.The digits are for current
carrying capacity. Here the mcb can carry 32 A of ac current
safely.
Now the alphabet stands for the type of mcb, taking
overloading and tripping time of mcb in account.
A for 1.5 to 2 times of overload current and tripping time
about 70 ms
B for 3 to 5 times of overload current and tripping time
about 50-60 ms
C for 5 to 10 times of overload current and tripping time
about 35-45 ms
D for 10 to 15 times of overload current and tripping time
about 20 ms
Generally for residential wiring we use D type for the
purpose of protecting from short ckt fault.
| Is This Answer Correct ? | 38 Yes | 6 No |
Answer / manikandan krishnan
First Digit A denotes tripping Curve and second two digits are rating of the breaker..Normally C curve withstand 7-10 time of FLC,D - 10-14 TIMES AND B CURVE is 3.2-4.8 TIMES OF FLC.
| Is This Answer Correct ? | 12 Yes | 4 No |
what is the synchronous timer ? and it applications.
What is K-rated transformer? What is the use of it? What can be the size(pls provide calculation if possible) of K- factor transformer for 550kW,690V motor operating with drive (VFD)?
why is the vector group analysis done in transformer tests
28 Answers K K Rao, Lloyds, Nicco Engineering Services Limited, Qatar Petroleums,
define main transformer?
What happens if i apply 500V to 440V rotary Switch ?
What is C check in a diesel generator and what are parts and what has to be done during the C check
if an induction motor is operated at unity power factor what will happen? will motor run or not? kindly describe a logical answer?
Why does the radius of armature is less than the radius of pole shoe?
what is the difference between mho characteristics and quadrilateral chara in distance protection
how many BUSBAR is in electrical system?
What are the different pre-commissioning tests that are performed on the distribution transformer, power cable and switchgear (11kv)?
what is vtg limit of earth and neutral at transformer side?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)