why we somewhere use ryb
phase sequance, somewhere
use uvw, and somewhere abc??
Answers were Sorted based on User's Feedback
RYB colors are used for phase indication
UVW are used in motor terminal connection.
By-Rajendra.V.Sawant
Miraj.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sheikh
R.Y.B denoted on the input side of 3 phase circuit
and U.V.W denoted on the load side like goes to motor
terminals etc.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.mubarak ali
for in my convinient thats all. i.e., in our country maximum
using of wire material this type of colour RED YELLOW BLUE
easily to find out the problem in transmission line so we
put RYB in three phase supply and also not wrong to mention
ABC UVW, thats it.,
Is This Answer Correct ? | 0 Yes | 1 No |
Distribution transformer we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral,we can not connect separate body earthing pit to other earthing pit but we do metal glanding in secondary side cable termination in both side, transformer and PCC panel (LT Panel), is this safe for transformer and other equipment?
how to select the rating of neutral ct with reference to transformer secondary current(in power transformer,stepdown tansformer,for example2000kva,11kv/415volt
why we use ac supply as 415 volts instead of 415 v why we cant apply 230 v for dc
xpression 'document.FrmQF.myemail' [
How can we explain that what is the power factor?
how much value of resistance should connect to 15 kw, 6 pole 3 phase slip ring induction motor having RV-240, RA-42.
how to select cable size?
Why we are testing a tan delta test in transformer? which purpose conduting that test? and time priode test?
How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me
When PRV operated at power transformer ,can anybody tell me particular pressure for 50mva transformer plzzz.
what is the cost of a analog tachometer, for lab purpose/
Q. calculate the value of the resistor to be connected in series with a 100W; 230V lamp so that the wattage of the lamp is reduced to 35W