I have calculated load for an office building which is 1200
KW
as all the load is single phase therefore its 1200 kw single
phase. Now i have to design Transformer and Generator for
this load Please kindly give me exact answer that how much
capacity of Three Phase Transformer and Three Phase
Generator is required for this load.
Answers were Sorted based on User's Feedback
Answer / mayadhar81
1200 kw = 1200*1000 watt
that means 1200000 watt ok
In single Phase for example 1000 watt load,supply 230
volts,current is watts/volts
answer is 1000/230=4.34 amps ok
in 1200000 watts =4.34*1200=5208 amps ok
Per phase current=5208/3=1736 amp
three phase transformer/ generator=1736/1.392=1247 kva dg
or transformer is used for full load.
Then you have used 1500 kva dg or transformer
and put it 80% load.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / niraj
Answer #1 does not take into account the power factor.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mahendra
KVA=KW/cosφ
KVA= 1200/.9
KVA=1333KVA @80%
KVA= 1500KVA
| Is This Answer Correct ? | 0 Yes | 0 No |
What are the Safety measures in central chiller plant? Explain them?
22 Answers Carrier, CPIC, HSL, JLL,
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
how many safety really of DG sets.
Why the motor take high starting current for long time(10- 15 sec) which is connected to Blower as compaire with a motor which is connected with pump with same rating?
What is state space method ? Why its used ? Can it applicable on linear, non-linear, 1st order, higher order, homogeneous, non-homogeneous, open-loop , closed loops , stable & unstable systems ?
kva/kvr
what is VSWR?
what are the industrail measures to overcome ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system? plz reply
How I design capacitor bank for different load.7MW connected load.
What is ST and specify its range of voltage.
what are the affects of loose connection in electrical circuit.
for ac networks if the voltage wave form is V=Vm sinwt here the voltage Vm=230 for the frequency 50hz then the time period is 0.02 sec then for the time period 0.12 sec what is the voltage
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)