I have calculated load for an office building which is 1200
KW
as all the load is single phase therefore its 1200 kw single
phase. Now i have to design Transformer and Generator for
this load Please kindly give me exact answer that how much
capacity of Three Phase Transformer and Three Phase
Generator is required for this load.
Answers were Sorted based on User's Feedback
Answer / mayadhar81
1200 kw = 1200*1000 watt
that means 1200000 watt ok
In single Phase for example 1000 watt load,supply 230
volts,current is watts/volts
answer is 1000/230=4.34 amps ok
in 1200000 watts =4.34*1200=5208 amps ok
Per phase current=5208/3=1736 amp
three phase transformer/ generator=1736/1.392=1247 kva dg
or transformer is used for full load.
Then you have used 1500 kva dg or transformer
and put it 80% load.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / niraj
Answer #1 does not take into account the power factor.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mahendra
KVA=KW/cosφ
KVA= 1200/.9
KVA=1333KVA @80%
KVA= 1500KVA
| Is This Answer Correct ? | 0 Yes | 0 No |
Recently we had experienced following problem All RCCB breakers (connected to the load as well as spares) connected to various UPS systems at various floors at a high rise building tripped during a power break down and upon starting up of generator.This Generator is recently inducted into the installation. Can any one explain the reason behind this tripping. Regards Viswanathan
when generator of a power plant is not connected to grid , by increasing the mechanical torque speed of rotor increases but when it's connected to load instead of increase in speed current increases , why?
What difference between voltage and current
what is real and reactive power?
why transformer comes only in standard rating like 11kv,33kv,66kv....and not like 33.33kv and so on?
how much load 15kva dg set can bear
what would happen when synchronous motor will operate beyond syncronous speed?
What is the formula for calculating impedance of transformers connected parallel at fault level 50KA?
Why do we use 36KV LAS for 33kv line and 9KV LAS for 11KV line?
we have a 2.5hp Starite electric motor water pump,the elec motor burned out,we need to replace starting capacitor(old capacitor specs erased),what microfarad rating capacitor do we need? 110-125V
the current which flows during lightening is ac or dc,,,,,,,,,,, WHY
Why we are designed only 11Kv and 6.6Kv Alternators, not 33Kv Alternators and Power Transmission side we are designed only 220kv, 120kv, 66kv, 33kv, 11kv, and 440volts, not 20kv, 50kv, 100kv.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)