In a Tap changing transformer where is the tap connected ,
is it connected in the primary side or it is connected in
secondary side
Answers were Sorted based on User's Feedback
Answer / suryaraj
Tapings are
connected to high
voltage winding
side, because of
low current. If we
connect tappings to
low voltage side,
sparks will produce
while tap changing
operation due to
high current. Not
depend on primary
or secondary.
Is This Answer Correct ? | 39 Yes | 0 No |
Answer / ronak panchal
tap changer is connected at ht side.
its not depend on primary or secondary winding but where the
ht side and lt side is been defined.
if primary winding is ht and secondary winding is lt then
tap changer will be at primary.
Is This Answer Correct ? | 18 Yes | 2 No |
Tap Changer is always installed at HT side,since at HT side
current is low .
reasons for not installation at LT side
1.high current
2.when we have to change the tap there is little bit
sparking, and sparking cause gas production ,thus buchhloz
relay operate.
Is This Answer Correct ? | 10 Yes | 0 No |
Tap changing are always provided in HV SIDE OF TRANSFORMERS
AS CURRENT IS LOW.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / vishnu vardhan singh thakur
its on secondary side. if it is placed on primary side and
when the voltage is increased magnetic core will be saturated
and if the voltage is reduced the magnetic core is not fully
used...... and mostly tappings are provided on HV side because
the current on HV side is less where it is high on LT side. so
when short circuit occurs no damage will happen thats y
tappins are provided on HT side
Is This Answer Correct ? | 1 Yes | 3 No |
Answer / deepak verma
actually we take o/p always at secondary side and tapping is used to adjust the o/p voltage, so tapping is done always at sec. side
Is This Answer Correct ? | 2 Yes | 8 No |
what is the function of AVR in generator? how the generator maintain the frequency while varies the load?
What is effect on in zone and out zone fault if CT chosen for phase side is Vk/2<5mA and Neutral side is Vk/2<15mA on REF protection of Transformer
what do you mean by star point.its importance in ct & pt
what is the other name of dc series motor
what is diode? and what it is used for ?
XYZ
why selected genration, transmission or any at 11kv, 132, 220, 220 or 440 voltage which is propotional to 11. why does not any for ex. 12 kv 13kv or any
11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The rated current is 26Amps. Application is for the blower. The motor takes ( no load without coupling impller ) only 2.5A and 5Amps in star & delta starter test.Need to know why its taking high current.
Why 11KV PT Secondaries [(11000/1.732)/(110/1.732)/ (110 / 3)]are in star connection ? And why the same should not be in delta ?
what phase and neutral.
What is STEP VOLTAGE ?
Load break swicth maintenance procedure.