why sec of ct should be kept shorted
Answers were Sorted based on User's Feedback
Answer / vishal ingle
the CT works on the principle of
Primary AT = Secondary AT
When current is flowing through primary, there must be
path for the secondary current to flow.
Else heavy ovevoltage will be induced in the secondary
winding which is sufficient for insulation failure and
busrcting of CT.
Hence CT secondary should always be short circuited
Is This Answer Correct ? | 5 Yes | 3 No |
Answer / k
The output voltage will rise trying to develop current until
it reaches the saturation voltage of the coil at that
frequency. At that point, the voltage will cease to rise and
the transformer will add no additional impedance to the
driving current. Therefore,the output voltage of a current
transformer will be its saturation voltage at the operating
frequency.
Is This Answer Correct ? | 0 Yes | 1 No |
In Aeroplane what circuitry or method use for earthing?
9 Answers Bhel, EDA, Wind World,
How is the Depth of Stator Slot being calculated for Synchronous Generator?
WHAT IS THE REASON OF CHANGE FREQUENCY IN DG SET AFTER FULL LOAD.
What are the significant parts of dc generator?
Why we can not get 100% efficiency from a Gas Generator?
Which phase is prefered for connecting 1phase vt used for synchronism in an OHL? why?
What is the effect of earth capacitance
WHAT IS THE MEANING OF CYWY
Why an ac solenoid valve attract the plunger even though we interchanges the terminal? Will the poles changes?
Brief use of isolation transformer & how it works.
why the emf of a cell more than the terminal voltage when the cell is delivering current?
What is the earth treantment procedure?