Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


HOW TO CALIBRATE A PRESSURE SWITCH?

Answers were Sorted based on User's Feedback



HOW TO CALIBRATE A PRESSURE SWITCH?..

Answer / rizwan

hi
procedure for calibration of pressure switch

for the pressur eswitch some set point is given for eg:
10 psi
so when we apply pressure to the pressur eswitch it should
get activated for that set point
the result sheet is written as

set point pre calibration post calibration
activation 10 psi 24 psi 10 psi
deactivation 30 psi 12 psi

the pressure switch adjustment is by some abjustment screw
or knob or according to the adjustment given in the preesur
eswithch.

Is This Answer Correct ?    27 Yes 10 No

HOW TO CALIBRATE A PRESSURE SWITCH?..

Answer / nanjilll

Procedure for the calibration of Pressure switch:

1.decide the required set point

2. check the switch contact is Normally Closed or Normally Open.

3.connect the multimeter between NC & Common and Select to continuity measurement.

4.apply the pressure by using hand pump or other pressure making tools(Hydraulic or Pneumatic)

5. check the change in continuity in multimeter.

Is This Answer Correct ?    23 Yes 7 No

HOW TO CALIBRATE A PRESSURE SWITCH?..

Answer / gireesh gokuldas

1)Obtain Permit to work. Confirm proper isolation of process.
2)Depressurize the system by draining or venting.
3)Disconnect the process tubing and replace with correct fittings for calibration with pressure source.
4)Wear goggles to avoid splashing of liquid into eyes when depressurizing.
5)Use a Digital Multimeter (DMM) set to the continuity range to check and verify that the switch contacts are as indicated: NO (Normally open) and NC (Normally close).
6)Connect the DMM between the normally open contacts (NO) and the common terminal (C) of the switch. The meter should read "open circuit"
7)Adjust the hand pressure regulator to increase the pressure to the set point of the pressure switch until the contacts change over.
8)The meter should now read "short circuit". Note the pressure reading and write it down. This pressure is the switch set point for a "rising" pressure.
9)Increase the pressure to the switch to its maximum rating.
10)Slowly reduce the pressure to the switch until the switch changes over from closed to normally open again.
11)Note and write down this pressure reading. This pressure is the switch setting for a "falling" pressure.
12)From the readings you have taken work out the pressure difference between the rising and falling pressure settings. This is called the "dead-band" of the switch.
13)The dead-band calculated should be equal to or less than the manufacturers’ dead-band
14)Disconnect the calibrator and restore the process tubing and put the switch in service.
15)Complete the calibration form and apply the appropriate calibration label.
16)Clean the area and clear Permit to work.

Is This Answer Correct ?    16 Yes 3 No

HOW TO CALIBRATE A PRESSURE SWITCH?..

Answer / sdsdf

It can be done sing a dead weight tester

Is This Answer Correct ?    10 Yes 4 No

HOW TO CALIBRATE A PRESSURE SWITCH?..

Answer / anish kumar

deside the required set point as per application
check the relay system which points are in contact
check the continuity of relays
select pressure source depents upon the range of the
pressure switch
apply pressure and observe the relay is off/on at which
pressure range

Is This Answer Correct ?    2 Yes 0 No

HOW TO CALIBRATE A PRESSURE SWITCH?..

Answer / parth desai

Steps as below :
(a)Set desire pressure.i.e for e.g 4 kg (bar)
(b)Keep multimeter's wire on 1 & 3 point of coil.
(c)Move nob with 5 num.LaN key in clockwise or
anriclockwise direction till you will get continutity.
(d) as you will get continutiy @ 4 bar ur input in PLC will
cut. now tight grub screw of pressure switch.now increase
pressure from 4 bar so you will get i/p on plc.

Is This Answer Correct ?    1 Yes 0 No

HOW TO CALIBRATE A PRESSURE SWITCH?..

Answer / rambabu

procedure for calibration of pressure switch

for the pressur eswitch some set point is given for eg:
10 psi
so when we apply pressure to the pressur eswitch it should
get activated for that set point
the result sheet is written as

Is This Answer Correct ?    6 Yes 9 No

Post New Answer

More Instrumentation Interview Questions

How to get Cv of control valve having following parameter ,i.e inlet pressure 4.5kg/cm2 outlet pressure 1 kg/cm2 specific gravity 0.808

3 Answers  


I have a problem with a valve (air to close). When it is fully closed and try to open 1% it doesn't responce till 3% open suddenly more than 3% then back to 3%. I tried to tune positioner then removed it, the problem still exist. Any idea

3 Answers  


Hi..i am B.E. (elect.&comm.)..i m workini in a bio mass power plant as inst. Engg. I want 2 know about growth in big power plant sector..is this field is good 4 me ..i m electronics engg..? Plz plz reply..

2 Answers   Reliance,


what is 24vdc live and dry supply

0 Answers  


What is difference b/w absolute & gauge pressure? EXPLAIN

2 Answers   IFFCO,


what is the tempareture conpensation?what is the use of this?

1 Answers  


How to Calibrate Flow Switch in field

0 Answers  


can i use capillary type dp transmitter converted to capillary type pressure transmitter. if i removed one side capillary tube its work correctly?

1 Answers  


Why shield is not connected at both end.

5 Answers  


how to connect transmitter measuring sulfur process? 1-by using long impulse line or 2- by using coated short impulse line

0 Answers  


Dear all, I'm manikandan I have done by DIPLOMA EEE from 2011 , I have 5 years of experience from Power plants instrumentation field , which one field is give long life & which one field is best ,I confused a lot And also I'm studying AMIE, can I choose which field from Section B examination?

1 Answers  


Area classification, Equipments, Gas groups, temperature classification, Ingress protection, Fire Extinguishers.

0 Answers   CCIE,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)