How to set an overload in a motor?
Answers were Sorted based on User's Feedback
Answer / vinod g
Over load relay is setting normaly at 100% of rated
current, also we can set at reduced current if load current
less and constant.Also overload relay have AUTO & MANUAL
Reset mode. ie in AUTO it get reset automatically with time
delay based on motor temprature reduction. Manual mode we
have to reset on every trip.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / siva24381
First we decide motor full load amphere(or name plate) and
take actual load amphere. If 3HP motor full load amphere is
4.5A but actual load is 3.0A so we set OLR rating 3.5A.
| Is This Answer Correct ? | 0 Yes | 5 No |
Answer / jaspreet singh
over load relay =1.5*full load current.example for 1 h.p
motor takes 1.5 Amp current so its overload relay is setted
at approximate on 2.5 amp
| Is This Answer Correct ? | 1 Yes | 6 No |
Saving in copper achieved by converting a 2 winding transformer in to an auto transformer is determined by A voltage transformation ratio B load on secondary C quality of core material D size of transformer core
Hi Recently I got one formula that is Impedence of Xformer = Rated KVA/Root 3 * secondry voltage OF Xformer. Is it Right??????
How does the slip regulator works as a startor
What is resonant frequency?
What is deference between MCB & MCCB & ISOLATOR
0 Answers Prakash Industries, Standard Chartered,
11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?
what happens when a dc shunt motor fed with an alternating suppy ?
what are all types of cross section in AC cables?
How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
1 Answers Ajanta Pharma, Bhel, Cosmo Films, Suzlon,
bit confused - am i correct in thinking that to determine line to line voltage in a star config 110v 3 phase 4 wire distribution system i would use a voltmeter? I have a circuit configured as an unbalanced load, consisting of three incandescent lamps (1x40w, 1x60w, 1x100w - all 110v rated)connected in a star configuration to a 110v 3 phase 4 wire distribution system. I want to find out what types of meters i would use to obtain: a) each line to line voltage b) the line to neutral voltage across each load c) current flowing in each line and load d) current flowing in the neutral conductor e) power supplied to the loads im assuming i would be using ammeters in series along each line and voltmeters in parallel across each line to neutral? Also how could i predict these meter readings before taking them and with which formulae? Any help would be greatly appreciated A.
the cheapest inducting instrument among all is a)pmmc b)moving iron c)electrodynamometer d)rectifier
Why the wave trap is put in Y phse only in switchyard?why not in other phases?
1 Answers IAG Automation, REL,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)