Why C.T secondary s2 done earthing?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
For safety against probable high voltage of primary
appearing in the secondary ,due to either insulation failure
or capacitive coupling between primary and secondary ,as
earthing has reference to the primary voltage.
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / tamilarasu
Incase sometimes we want to change the ammeter or any c.t
using relay that time we shorted the s1,s2 tappings. incase
we forget the short of s1,s2.same time c.t burned& it
produce some dangers .so we reduse the danger from c.t
regarding the earthing
| Is This Answer Correct ? | 6 Yes | 6 No |
Answer / henry vakharia
Current transformers are classified in two categories viz.
protection and measuring classes.
In protection relay, the earth fault is detected from the
earthed terminal or say the common terminal shorted
together and then grounded, which makes the relay detect
the earthfault other than its core function of protecting
equipments from high voltage surges.
In measuring relay, the C.T. is grounded to give protection
from the primary high voltages surges.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / d.lakshmi narayana
IN HT IN CT SECONDARY SOME VOLTAGE GENERATED.THIS IS ACTUAL
CONDITION. IN FAULT CONDITION IT IS INCREASED. ON THT TIME
CURRENT OPERATED COIL IS SOME TIMES IT WAS DAMAGED OR
SUPPOSE U R USING INTEGRATED RELAY SOME TIMES IT WAS DAMASED
THAT'S WHY THE CT SECONDARY IS EARTHED OTHERVICE MORE
VOLTAGE IS COMIG SOME TIMES THE CT OPERATED RELAY WAS
MALFUNCTIONING.
SO CT SECONDARY IS EARTHED
| Is This Answer Correct ? | 2 Yes | 5 No |
Do you know the overhauling of a motor?
suri transmission
1. A 380 / 220 V r.m.s. 3-phase 4-wire circuit carries loads of 8 + j8.1 ohm; 4 + j4.1 ohm; and 2 +j2.1 ohmin the three phases respectively. The length of the circuit is 100 m, and the resistivity of the phase conductors is 0.0005 Ω/m. The neutral conductor is of the same size as the phase conductors. a) Select a reference angle 0for the first phase. Then write down the three phase voltages in both polar format and complex number format. b) Make appropriate assumptions, and take temperature effects on resistance is insignificant. Calculate the currents in the three phases. (Note: Determine conductor resistance, and apply Kirchhoff’s Voltage Law) Based on the result, suggest a main switch rating for the circuit. c) Show your preferred direction of neutral current in a diagram, and then determine its value. (Note: Apply superposition principle, and Kirchhoff’s Current Law) Use its magnitude to show that in this circuit, the unbalanced load may increase the voltage drop in some of the phases. (Note: Also observe the common volt drip in neutral) State your assumptions, if there are any. d) Suddenly the neutral wire of the circuit is broken. Estimate the new currents in the first phase, i.e. Phase L1. State your assumptions, if there are any.
hi sir i have load of 17.5kw in 3 phase lighting circuit which mcb i can use
why vector group is ued
diffance between eletrical and eletronics?
where are the circulat the diesel in DG parts name with pictue
What is C2-M2-E2 class in circuit breaker. why and where it is to be used in circuit breaker
what is non uniform load
How to implement 6 output with 3 input NAND gate?
how to difference between the HT< cables
please send me previous year questions of jspl through which i could prepare myself for the test.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)