What is the size of cable to be used for a Space Heater in
UPS 160KVA of carrying 10 Amps current with 240 V ,1 Phase?
Answers were Sorted based on User's Feedback
Answer / pillay
For a load of 10 amps a 2.5 mm sq cable protected with a
suitable breaker should be good.
| Is This Answer Correct ? | 2 Yes | 0 No |
What is the difference between ground & earth or neutral
how to caculate no load loss, load losses & impedance percentage in power or distribution transformers
WHAT HAPPEN WHEN CT SECONDARY OPEN DURING LOAD
How to make two bulbs glow Alternatively?
two TG running in parallel at equal load.one TG CB tripped in reverse power relay.after tripping found its excitation was on & turbine running at rated speed.Please clearify why that TG tripped in reverse power ?
Which motor will you choose which can operate in both lagging as well as leading power factors?
errection check list for transformer maintenance
is any body explain me why return current in three phase power system is less then in a red, yellow, blue phases??? as we know Ir+Iy+Ib=In then why nutral wire has less then phase current????
WHY DOES NEUTRAL DO NOT CARRY EVEN THOUGH IT CARRIES RETURN CURRENT?
What is distance protection relay? where & why we use this relay?
2 Answers Siemens, UltraTech, Voltech,
in the exciter the power is feeded from battry or control or whatever.and we need it in the generators for the stating . do we need it in the shutdown also?i mean the exciter>
HOW CAN I GET 5CORE HO7 CABLE SIZE IF I HAVE 1800A?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)