why do we prefer a 3-phase delta connected load rather than
star connected?
Answers were Sorted based on User's Feedback
In star speed of motor is very low with low amp.
and in delta motor running with its normal rated speed with
rated amp.
So generally for motor starting purpose star used and
afterthat its change over to delta
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / nithi
for a same power rating the current in delta connected load
is 1.732 times lesser than the star connected load (heat
loss is less) &also if one phase get opened the other two
phases will serve the load i.e.good stability.but in safety
point of view, star connected load is better than delta
load.because earthing can be done without the help of
earthing transformer.
| Is This Answer Correct ? | 3 Yes | 1 No |
Dear Subhash
Yes speed of motor will remain same in star and delta both
| Is This Answer Correct ? | 0 Yes | 2 No |
HOW TO CALCULATE AMPs OF CURRENT TRANSFORMER IN HT Panel
Explain the iniluencc of short circuit ratio on the pert'orniancc of synchronous machine.
in 31.5 mva power transformer how to set of wti and oti?
In scott connected transformer number of turns in the primary winding of teaser transformer is % of number of primary turns of main transformer A 86.6 B 57.7 C 14.4 D 33.3
What is fault level? How can be calculate the fault level?
how DC motor operating in detail .pls any one guide me .iam not clear idea about that .thank u
Can earth resistance be measured without connecting the earth electrode? and should earthing connections be disconnected What is the effect of connecting two cables of different sizes in parallel with supply? Thanks in Advance. I am intrested to get in touch with some tecnocrats/engineers,my mail i.d is : hiremathvijay@rediffmail.com
For the requirement of a furnace of temperature range up to 1200 oC using silicon carbide rods, What is the required rate of transformer needed (please do it with all details)?
A Generator is in running condition and Rotor earth fault alarm is coming.How to check on line(i.e in running condition) whether there is actual earth fault in rotor or not.
In Swinburne's Test on D.C.machines, why the efficiency is more when the machine runs as generator than when it runs as motor???
6 Answers College School Exams Tests, GE, MVR, Practical Viva Questions,
why shoud in High tension cable( above11KV etc.,)a semiconducting material coating will be there on insulation?
can we run three phase motor by single phase? and what happens if we do this
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)