what does happen if generator frequency fall in running
condition & what should require immediately
Answers were Sorted based on User's Feedback
Answer / kailash
Either we have to reduce load or we have to increase speed
of prime mover by increasing fuel (diesel/steam) through
governor.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / poorna
if the generator frequency falls during running condition
it may result in circulating currents if it running in
parallel with other generators or it is connected to grid,
remedy is to increase the speed of prime mover by any means
if not possible reduce the load
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / siva rao
the emf induced in alternator will reduced to very low value
and the generator will not serve any load.if the frequency
will fall to a lower value the excitation of the generator
must be increased.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / mahi&junu
there are two methods. Either we can decrease the load connected or we can increase the excitation
| Is This Answer Correct ? | 5 Yes | 3 No |
why colour of electrical equipment( like transformer) is grey
it is in our knowledge tht right plug of supply of residential suppy system is phase n other is neutral...howevr the battery charger of mobile works in both ways...i mean it is not restricted in only one direction.ny of the holder of charger can hav phase .so y is it not lik tht phase of supply must b connected 2 phase of charger...?
WHATS THE DIFFERENCE IN USING THE 125% AND THE 250% FACTOR OF SAFETY IN CALCULATING CIRCUIT BREAKERS CAPACITY IN MOTOR APPLICATION??
Why one side of secondary of transformer is earthed, to supply single conductor of electric traction system?
why we cannot protect 100% winding of an alternator by using differential protection?
How do you classify the different types of torques?
what will happen if a 3 phase motor is connected to a single phase circuit and vice versa?
What is function of Diesel Generator?
How amny AH battery required for 600va inverter ?And how many hours it will give backup for ceiling fan ?
What is the rating factor for copper cable ( Specific value according to the type of laying ) & the voltage drop?
In 6600/√3/110/√3v voltage transformer,how much output voltage in open delta transformer,after removing 1-phase of primary side on transformer?
which relay is used on long transmission lines
10 Answers ABB, Bhel, Student, Tata Steel Limited,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)