sigal phase supply is 230 v ac
two phase supply is 415 v ac
why three phase supply is 415 v ac why not 690 v ac
Answers were Sorted based on User's Feedback
Answer / prmeghwanshi
Because you measure voltage between onlt two point like RYB
when you connect N to any other RYB then voltage is 240V
(App.) this is called single phase.
when you connect one point into RYB(R) and other is also RYB
(other than R) is 440V this two phash. when you use three
phase voltage is measure in only two point like R to B R to
Y so it is also 440V. you can't measure voltage betwween
three point.
| Is This Answer Correct ? | 15 Yes | 4 No |
Answer / vasi
If Phase-Neutral voltage is 230v then Phase-Phase voltage in
3ph system willbe sq.root of 3 X 230v
The 3 ph are displaced 0-120-240 degrees and the Pitagor
Theorem can be used to count up the Line voltage
Another way to count up the Line(Phase-Phase) voltage is to
use vector analysis
1st Phase 0 degree 230+j0
2nd Phase 120 degrees cos120*(230) + sin120*(230) this gives
-115+j199
3rd Phase 240 degrees cos240*(230) + sin240*(230) this gives
-115-j199
in the end ph1-ph2 398v, ph1-ph3 398v, ph2-ph3 398v
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / arvind
its a very good question, see what we r measuring is phase
to phase voltage, in case of 3phase system,that means
beetween two phase is simple because we have two points of
voltmeter to measure the voltage.
| Is This Answer Correct ? | 1 Yes | 5 No |
can i use 2000/5A Clamp meter to measure HT cable
what is ohms law?
Can anybody tell me the Electrical IS rules website?
why we use ac supply as 415 volts instead of 415 v why we cant apply 230 v for dc
After synchronizing the running generator with grid, the avr getting tripped and the generator breaker also oettong tripped, before tripping the avr the pf meter of generator is showing leading pf please kindly give a suggestion to rectify this problem.
what is use of lockout relay in ht voltage
If we have a 2000kva load,How much kvar capacitors we go to add to improve the power factor at 0.9?pls give the calculation and fully theory?
Can we use MCCB with Auxiliary Contact in place of Contactor in a AMF System.
How to test lightning Arrester?
why dc is used in control circuits for MV & LV switchgeras instead of ac
Explain what is CBCT.
What is lighting kitts.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)