Answer / k.prakashchandra
The existing pf is not given.Use the formula KVA2=KW2+KVAR2
and KW/KVA=pf
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / n.sinha
The calculation we follow is :-
(kva)2 = (kw)2 + (kvar)2
and the P.F is given as 0.9,
so, kw = kva * P.F
= 2000 * 0.9
= 1800
And, kvar = {(kva)2 - (kw)2}1/2
= {(4000000) - (3240000)}1/2
= {760000}1/2
= 871.78
| Is This Answer Correct ? | 1 Yes | 5 No |
What is the actual calculation for transformer short circuit test?.
Explain few advantages of electric traction system?
can v rotate single phase induction motor in both the direction...?
list of tests to be carried out at manufacturers end while purchasing a step up transformer of 11kv to 66kv ,2MVa Capacity.
How much earthing frequency is capable?
1.ZEBRA conductor(large size) 2.KUNDHA conductor( small size ) 3.panther conductor(very small ) 4.lepard conductor (very very small)
what is the different between DC & AC load Line.
How Self works in DG set
WHY SECONDARY OF CT SHOULD NEVER BE KEPT OPEN CIRCUITED?
Can a generator rated 400 V, 60 Hz be used in a 50 Hz System? Yes or No ? Why ?
who is invented transforner (230v).......
What is the difference between KW & KVA ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)