what is the purpose of %impedance for transformer
Answers were Sorted based on User's Feedback
There are two basic purpose of % impedance of transformer.
1. We can check the fault level of the transformer.
2. During the parallel operation of transformer, both transformer % impedance should be identical for load sharing. other wise which transformer has less impedance it will take more load.
its the basic need of parallel operation for two transformer.
Is This Answer Correct ? | 9 Yes | 0 No |
Answer / guest
%impedance is to know the short circuit current of
transformer,depend on transformer ratings , for ex: 1600kva
6%,20 mva 10%
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / suseendran
It is the output voltage drop when transformer is fully
loaded..... This can be measured by conducting short circuit
test.....
Is This Answer Correct ? | 0 Yes | 2 No |
Why dont we get shock while testing for voltage with a line tester? How the bulb inside the tester glows while testing with tester coz we are totaly isolated from earth or we are not giving close path for the current to flow?
what do you mean by PF correction. A motor is rated at 15 kw,415 volts, 0.7 pf and eff of 0.92. The powerfactor is improved to 0.98 by adding capacitors at the bus. calculate the current drawn by motor under full load condition before and after pf correction
Between educational qualification and practical work experience, give us a brief explanation on your practical experience in your past Endeavour that you performed well to the satisfaction of your past or present employer?
Which starter can be used for 3 phase verriable speed (2 stator wdg) induction motor ?
When PRV operated at power transformer ,can anybody tell me particular pressure for 50mva transformer plzzz.
what is the use of neutral displacement relay
In an electrical conductor, if current flows because of flow of electrons, then why not the conductor gets thinner day by day???
WHY THE RATINGS OF TRASNFORMER IS IN KVA?
What will happen if I apply DC to AC transformer? please send detailed answer at habib_rahman_habib786@yahoo.com
why we somewhere use ryb phase sequance, somewhere use uvw, and somewhere abc??
If 100 KAV USP dedicated earth got disconnect / Cut. What will happen at load.
tell me about eletrical contractor