1.what is the difference between MPCB and MCB ?
2.what is the difference between MPCB and MCCB ?

Answers were Sorted based on User's Feedback



1.what is the difference between MPCB and MCB ? 2.what is the difference between MPCB and MCCB ? ..

Answer / george m s kingsley

Hai dear engineers,

MPCB- Motor Protection Circuit Breaker

It breaks the circuit depend upon the properties of the machine.
eg:- Set the breaking current of 10Amps in MPCB for the
Machine rating of 10Amps.
So that the machine take the starting current of 1.3 to 1.5
times from the rated.MPCB does not react here. But if the
current goes 120% to 150% based on time duration it breaks
the circuit.(overload relay supportive to machine)

MCB- Miniature Circuit Breaker.

It doesn't bother about Machine. If the Ampere goes more
than the MCB range it breaks the circuit.
Short circuit protection
(overload relay supportive to resistive, lighting load,
control circuit etc.)

Is This Answer Correct ?    54 Yes 10 No

1.what is the difference between MPCB and MCB ? 2.what is the difference between MPCB and MCCB ? ..

Answer / saroj kanta nayak

1.Both MCB and MPCB protects against Short circuit and Over load. But MPCB is better for the more starting current taken by Motor. and the Current range can be ardjusted. In mcb we cannot ardjust the current.
2.Both MPCB and MCB protects against Short circuit and over load. But the main difference is MCCB have NO & NC contact built in which used for the control circuit. untill and unless MCCB made on control circuit cannot made on(for motor starter feeder) In camparision to MCB, MCCB have higher current rating. And if current rating increases ACB(air circuit breakers used).

 So in conclusion All MCB,MCCB & MPCB gives the same protection even can be used in any others place. But MPCB is best for MOTOR protection as it have Inbuilt OVER LOAD RELAY and current range can be selected. Others(MCB&MCCB) may give trouble of unnecessary tripping during starting of motors.For short circuit protection all devices like MCB,MCCB&MPCB functions similar way.

Saroj kanta Nayak
SIEMENS LTD.
KALWA,MUMBAI
Masters In technology from
Nation Institute of technology, Silchar.

Is This Answer Correct ?    30 Yes 2 No

1.what is the difference between MPCB and MCB ? 2.what is the difference between MPCB and MCCB ? ..

Answer / chetan

MPCB-MOTOR PROTECTION CIRCUIT BREAKER
MCB-MINIATURE CIRCUIT BREAKER
MPCB TOTALY DIFFERENT FROM MCB AS IT IS NOT ONLY SIMPLE
CIRCUIT BREAKER AS MCB IT HAS INBUILT OVERLOAD RELAY RANGE
IF THE LOAD ON THE MOTOR EXCEEDS ITS CURRENT ABOVE THE
LIMIT OF MPCB IT TRIPS.
MCCB-MOULDED CAGE CIRCUIT BREAKER
MCCB IS A CIRCUIT BREAKER HAVING HAIGH LOAD CAPACITY THAT
IS ABOVE 63 AMPERE WE ARE GENERALY USE MCCB INSTED OF MCB

Is This Answer Correct ?    15 Yes 7 No

1.what is the difference between MPCB and MCB ? 2.what is the difference between MPCB and MCCB ? ..

Answer / rohan

MCB(Miniature Circuit Breaker) which ranges from 0.5A to
63A, but now HRC MCB has rating upto 125A, anything higher
than this rating requires a design which can handle so high
current so MCCB(Moulded Case Ciruit Breaker) which has raing
upto 1000A, whereas, MPCB is used for Motor Protection Device.

Is This Answer Correct ?    9 Yes 6 No

1.what is the difference between MPCB and MCB ? 2.what is the difference between MPCB and MCCB ? ..

Answer / amu

Dear George M S Kingsley
plz tell me what is the diff b/w lugs and thimbles in electrical field.

Is This Answer Correct ?    2 Yes 1 No

1.what is the difference between MPCB and MCB ? 2.what is the difference between MPCB and MCCB ? ..

Answer / rajesh

MPCB means motor protection circuit breaker.its called
manual motor starter.its not a motor its also protective
eqiupment.its working range is 0.1A-25A.MCB(miniature
circuit breaker)and MCCB(molded case circuit breaker)
working range is from the above 10A.

Is This Answer Correct ?    9 Yes 18 No

Post New Answer

More Electrical Engineering Interview Questions

Why is negative feedback invariably preferred in closed loop system?

0 Answers  


Why we should use delta connection in primary and star connection in an distribution transformer, which converts 400v a.c. voltage to 33kv.

15 Answers   ABC, Kirloskar, Sify,


Is it possible to convert Dependent sources to its equivelent current or voltage Sources ?????

1 Answers   Zen Technologies,


what is the purpose of measuring % impedence?

1 Answers  


In three phase energymeter the spindle rotating backward why?

1 Answers  






7/20,3/20 electrical wire is specified as stated.Why?

1 Answers   TCS,


how many BUSBAR is in electrical system?

3 Answers  


What is the need of earthing transformer for delta side of a transformer. (Think of a line section between a star/delta transformer at a grid substation and delta/star transformer at a village. An earthing transformer is there at the delta side of the star/delta transformer at grid substation). As there are no ground reference there will not be fault current if a one phase is grounded. Further L-L phase will be sensed by the primary side of star/delta transformer as a L-G fault. So why an earthing transformer is required at delta side

0 Answers   CEB,


To measure insulation resistance of 11KV cable between core & armour, what should be the test voltage & duration?

4 Answers  


what is load shedding

4 Answers   KSEB,


It is being often experienced that due to single phasing fault of any source transmission line of any closed loop synchronized circuit all the power transformers with primary stared trips but the power transformer with primary delta wont, why ?

1 Answers   MSEB,


Is there any particular formula for sizing the bus bar based on the current rating

1 Answers   Bunt Solar,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)