how to calculate the megger values for motor, cables and
transformers?
Answers were Sorted based on User's Feedback
Answer / karan
The thump rule is voltage rating +1 example for a 11KV
motor it should be 11+1=12 Mega ohm.
In addition to that the PI is the ratio between 1Mnts and
10 mnts.It should be above 1.5
For examle IR at 1mnts= 10M.ohm,
IR at 10 Mnts= 20 M.Ohm
Then the Polarisation index is 2 which is consdierd
good.When it is below 1.5 you can heat the tranformer or
motor then the value will come up.
Is This Answer Correct ? | 25 Yes | 4 No |
Answer / priyan
see sundar
Meggering test is done for any electrical equipments to
find the insulation resistance value.
As per the standards for testing the machines 3 methods are
there
1)spot reading 2)time-resistance testing method 3)step
voltage test
the following is the second mehtod it is in use nowadays
PI=10 min/1 min value
Then the Polarisation index is 2 which is consdierd
good.When it is below 1.5 you can heat the tranformer or
motor then the value will come up.
Is This Answer Correct ? | 15 Yes | 4 No |
What are the main faults of DC generators?
0 Answers Mercantile Marine Department,
What is Procedure the procedure to select CT's & PT's in 66kV and above substation?
3 Answers Infotech, Vijai Electricals,
What are the effects of armature reaction on a DC machine and discuss the various methods to reduce the effect.
what types of load we get from the national grid? is this capacitive or inductive?
what is function of centrifugal switch in single phase induction motor..?
In power generator sets, when they are coverted from 50hz to 60hz, the kva rating after conversion increases. For example, the manufacturer of a perkins 200kva @ 50Hz generator set has mentioned it to become 220kva after converstion to 60hz. What is the relation between the frequency & the KVA rating. Any formula please.
earth also having a gravitational force (magnetic field of north and south)but it attracts any object compare to this theartifical magnetic cant perform same as earth why?
how is positive, negative, zero sequence is happen.. how is effect on 3 phase system
I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency 75%(star delta connection)Motor. How to calculate line current & Phase current (1) Star connection (2) delta Connection
what is tha between elcb & rccb?
in 400 kv system why should trip both side CB when we give hand trip?
what is droop?