how to calculate the megger values for motor, cables and
transformers?
Answers were Sorted based on User's Feedback
Answer / karan
The thump rule is voltage rating +1 example for a 11KV
motor it should be 11+1=12 Mega ohm.
In addition to that the PI is the ratio between 1Mnts and
10 mnts.It should be above 1.5
For examle IR at 1mnts= 10M.ohm,
IR at 10 Mnts= 20 M.Ohm
Then the Polarisation index is 2 which is consdierd
good.When it is below 1.5 you can heat the tranformer or
motor then the value will come up.
| Is This Answer Correct ? | 25 Yes | 4 No |
Answer / priyan
see sundar
Meggering test is done for any electrical equipments to
find the insulation resistance value.
As per the standards for testing the machines 3 methods are
there
1)spot reading 2)time-resistance testing method 3)step
voltage test
the following is the second mehtod it is in use nowadays
PI=10 min/1 min value
Then the Polarisation index is 2 which is consdierd
good.When it is below 1.5 you can heat the tranformer or
motor then the value will come up.
| Is This Answer Correct ? | 15 Yes | 4 No |
What is difference between ct&pt transformers?
75 kw motor take 45 amp in no load delta in star 10 amp but in load it will take 160 amp but IR velue of winding above 500 at 1kw ph to earth and ph to ph. what problem it should be?
What are the different types of VVVF Drive ?
how to calculate current carring capacity of cable and cable selection? 1) copper flexible cable 2) copper armoured cable 3) Aluminium cable
What is the calculation for 1000Amps Air circuit breaker relay settings.
TNC switch is also available in 1NO+1NC. What does it mean ?
List of equipments required foe industrial repair lab.
respected sir, sir recentely i have applied for chennai and tiruvananthapur section enggineer and juniour engg in electrical dept. but still i donot get how i have to syart my preparation and also t the same time i donot know exactly what they r going to give in the examinations i mean which sections they r going to give i donot know exactly, can u prefer whichh books i have to follow and model papers or both boards
neutral carrying current more than phase in 3phase supply.i want to know the reason?
How calculate the Transformer Impedence With Example
What is the use of mc( moving coil) in dc voltmeter and dc ammter and what is the use of ( moving iron)in ac voltmeter nd ac ammeter
why we use ac supply as 415 volts instead of 415 v why we cant apply 230 v for dc
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)