why neutral and body earthing of transformers kept
separated? what is distance between two is required as per
is?
Answers were Sorted based on User's Feedback
Answer / pramod sawant
1.Body earthing is used for body leakage current to earth &
not human body harmful.
2. Neutral earthing is used for
unbalance current pass through neutral & its goes to earth
& not effect on other phases voltages/load.
| Is This Answer Correct ? | 32 Yes | 3 No |
Answer / ashish jani
body earthing used for transformer leakage current to avoid
human injury and use for transformer protection.
Neutral earthing used for transformer unbalance current of
transformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / vimal
It's not neutral earthing.its called neutral grounding. Like NGR NTR
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / brijesh
Body earthing is ued for earth the leakage current passing
through equipment body. the other purpose is to protect
human body against passing the leakage current.
Neytral earthing is used for giving an earth path to
unbalanced current. It also ballance the voltage in each
phase.
| Is This Answer Correct ? | 2 Yes | 1 No |
if not separated,suppose neutral is not working
properly,then in case of lightning on the body of
tranformer then very large current will flow through body
earthing wire to neutral earthing wire.So it will be
dangerous for transformer.
so to avoid from destruction both body earthing & neutral
earthing are separatly properly earthed.
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / engr.shahbul
Body earthing is used for body leakage current to earth without
human body harmful.Neutral earthing is used for giving an earth path to
unbalanced current. It also balance the voltage in each
phase.suppose neutral is not working
properly,then in case of lightning on the body of
transformer then very large current will flow through body
earthing wire to neutral earthing wire.So it will be
dangerous for transformer.
so to avoid from destruction both body earthing & neutral
earthing are separately properly earthed.Minimum 3meter
| Is This Answer Correct ? | 1 Yes | 0 No |
What do you mean by a phase angel of instrument transformer?
a room heater is connected in serise with a 100w bulb.if the 100w bulb is replaced by a 40w bulb then the output of the heater is increase/decrease/remain same?
9 Answers College School Exams Tests,
what is slip ring startor
what is working of Master trip relay ?
when a motor is connected in parallel with the existing motor the pf will change or not?
will a fluorescent bulb work when dc is passed through it?? if not why??
whow we find out dc motor field aur armature resistance
what is gapless metal oxide techniques?
Why we use Electrical energy rather than any other type of energy, mostly? Explain behavior of open secondary CT and short circuited secondary PT in energized condition?
Why PT voltages are measured with respect to ground? What do u mean by voltage or current polarized.
when we start the tube light, then it takes initially 1100 volt, after glow it takes 120 volt?(when we give 220 volt a.c.)
Hi,iam a diploma in electrical engineering.rtd from indian air force in apr 2007.prsently working in reliance next link as a network maintenance engineer since 2007,can i get a job in motherson sumi.
0 Answers Motherson, Motherson Molds and Diecasting Ltd.,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)