Can neutral line also be use as a earthting for
distribution transformer, or we need separate earthing pit
forh the transformer?
Answer / ullas
in the distribution transformer the secondary star side
common point is earthed and taken it as a neutral terminal.
this neutral is earthed 4 place i one mile., in order to
keep the potential as zero volt..
there are so many distribution systems in india.
take the case of kerala, my state.
here we are using the TNCS System.
here phase line and neutral line are given to the consumer
by the supplier. the consumer shall provide an earth pit
for earthing his equipments.
in tamilnadu the TNEB provide additional earth line with
phase and neutral.
Is This Answer Correct ? | 7 Yes | 0 No |
Can the same motor be operated in both direction ?
LT cable fault checking instrument is available? where and how to get it.
What is the difference between bundled conductors and double circuit?
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
what is the disadvantage of lagging power factor & why ?
What's the difference between non break power supply and non break non short break power supply
If the generator will not synchronize, what will you do?
what is the dis-advantage of 3 phase 3 wire energy meter?
suppose we using 3 phase motor of 440 v means what range of C.T. is require for measuring current , the rating of motor is 1HP ?
which fault is severe and why?between lll fault and lllg fault which fault is severe and y?
when the direction of a 3phase induction motor is reversed , is there any losses increases?
Can we use same copper cable for both AC & DC power.