if power factor comes in leading & showing -0.95. Is there
any effect on electrical system? if yes, then please tell me
what would be the effects. & how long we keep power factor
in leading.
Keeping power factor in leading shows more KW & less KVA is
it correct or not.
Answers were Sorted based on User's Feedback
Answer / santosh kawade
It is not recommended to keep power factor leading:
1) We try to keep power factor unit to reduce transmission
losses, this main purpose will not achieved by keeping
leading power factor. If power factor is lower than unit
(it can be leading or lagging) transmission loss will
increase.
2) During leading power factor if we make any breaker
operation (close/open)it will generate high voltage across
breaker, which is harmful to breaker. For capacitive load
operation we need a special breaker.
3) It is not correct that keeping leading power factor
shows more KW and less KVA.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rahamadulla.m
Yes there is effect on electrical system.The power will be
lost and could not maintain the voltage in the capacitor
bank system. so we can keeping power factor in leading
shows more KW and less KVA.It is correct.
| Is This Answer Correct ? | 2 Yes | 2 No |
how to calculate knee point voltage of current transformer?
21 Answers Bhel, Bhilai, Jackson,
Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR) Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,
WHAT ARE THE FACTORS REQUIRED FOR SELECTION OF TRANSFORMER RATING?
13 Answers Tech Mahindra, Technip,
what is size of 3phase 4wire cable to be used for 11 ton ductable A.C and how to calculate cable size for different load
how the phase convertor changes the no. of phases
in domestic service connection,what is service main?
In case of a synchronous generator carbon brushes, some brushes expire before the others. Why is so? When all the brushes are installed at the same time, why don't thee expire at the same time?
what the is the distance between 110kv termination point and the ground. how to calculate
how the earthing point or earthing is taken for ships and airplanes?
Hot Water System (HWS). Will a 30ma elcb have more nuisance tripping than 100ma elcb
I have CNC Turning lathe,while doing electrical preventive maintenance what should I do & please brief me plan & shedule for the same.
what is IP65 & What is its advantages
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)