Answer / santosh kawade
Three phase motor differential relay testing can be done
with single phase test kit.
There are two type of relay testings:
1) Primary injection : In this testing entire system
(including relay, control wiring and power wiring get
checked),
2) Secondary injection : In this testing generally we check
relay only.
By using single phase test kit:
1) Primary injection :
a) Carryout shorting of all three phases of motor winding
by using short link for individual phases seperately.
b) Inject current by using current injection device (for
inzone and outzone fault)
3) Check stability of relay for outzone fault and operation
of relay for inzone fault.
2) Secondary injection :
Directly inject fault current in relay terminal and check
proper operation of relay.
Santosh Kawade
9224 69 3116
| Is This Answer Correct ? | 6 Yes | 2 No |
Who many reason of ignition fail ?
how to calculate the slowness and fastness of energy meter if we have different kw load for example (0.746 kw and meter rev constant 400 and we calculate the 2 rev in 30 sec) please explain the formula thanks
1 Answers WAPDA Water and Power Development Authority,
How many types of losses occur in a transformer?
What is harmonics in AC waves. How it is generated? How it will effect the system network? how can eliminate it?
We have 90mX100m hangar with 16 no.of supporting pillar. It is required to provide power supply on all pillars. what is suggested earthing scheme for hangars.
what is the difference between NC & CNC machine.what is the difference between equipment & machine tool
what is the difference betwteen overcurrent and short circuit fault?
What is the maximum load an electric engine can pull??
What is inverse definite minimum time lag relay? Where is it use?
How can CALCULAT the current carrying capacity of aluminum and cOpper cables respective of that Sq.mm ? with formulas ?
12 Answers Bajaj, Eagle, Godawari Power and Ispat, Havells, L&T, Mascot, Polycab, SGML, Sterling Wilson,
why does the time taken for fuse to melt is longer as the wire length increases?
what is difference between 5A and 100A CT constructional wise and operation?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)