Answer / dinakaran
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
Is This Answer Correct ? | 33 Yes | 2 No |
Answer / vinod
Neutral CT is connecting between the neutral of transformer
and earth.(neutral bush of T/F to CT P1, CT P2 to earth).
This CT (PS Class) out put is using for REF (Restricted
earth fault protection of transformer winding)ie.REF is
operate only winding earth fault
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / md ekram
Normally neutral is connected to the earth.In that neutral
line we are connecting ct bcoz of sensing the earth fault to
protect the transformer winding against earth fault.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / amal raj
neutral is connected to the earth.In that neutral
line is connecting ct for sensing the earth fault to
protect the transformer winding against earth fault.
Is This Answer Correct ? | 2 Yes | 0 No |
when we megger is not damaged when we are measuring very low resistance? high d.c. voltage is produced in megger so according to i=V/R. current will be high so what is the reason ?
what is the surge arrestor?how it operates?what is the range for it?
how the testing of protection CT Testing done through Primary injection kit please describe in detail procedure...
what is vfd?
what is the acceptable earth resistance value ?
How can I calculate per unit (KWH) fuel (Gas/ Diesel both) consumption 1MW unit?
Why CT secondary is grounded?
What is the si unit
why do we put a transformer on soak before loading it
if 20 hp motor starts directly stars and contenious run . what will be the effect.
11 Answers HP, Ohsung Electronics,
What are the voltage values for LT,HT,EHT and other voltages??
If one 10 Hp 3phase induction motor connected in 380volt 50Hz. and again its connected to 380volt 60Hz. howmuch currrent and power take on both time?????