Answer Posted / s c budhiraja
Yes, this transformer is large enough for the house in
question.A normal house requires 100w/sq.meter area
including Air conditioning.The 930 Sq.meters reqire:9300w.
and add 10kw power reqired for the SPA. So total power
reqired is 19.3KW.A 25kva Transformer can supply power of
20kw at naormal power factor of 0.8. So the transformer is
is large enogh to meet the power requirement of the house
in consideration.
Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
what do w do when the output of generator is fluctuating?
how to control dc motor?
Please explain me about Relay curves and their sources to read ?
WHY SEPARATELY EXCITED MACHINE NEEDS EXCITATION BY DC SUPPLY WHY NOT BY AC
What is meant by earthhing of a magnetic flow meter and when to use empty pipe detection?
how to measure dc earth leakage current?
my diploma certificate in my higher education college
What are the advantages of instrument transformer?
Can an inverter be used as a converter? How?
how is the connection of a 3 phase ct trivector meter done on a pole mounted transformer
size of condotory fron voltage level
do you have some of interview Questions in power and genrator section in general whith answers
what happen when increase or decrease size of lamp,light.glass.
in ring main system we use the isolater b/w transfer bus and main bus if we r not use isolatar than wat will be the effect in our sys.
after how many spot we must chang secondry cable in portable spot welding gun?