why we used capacitor in induction motor?
Answers were Sorted based on User's Feedback
Answer / m s kumar
Since induction motors have inherently low power factor,
Capacitors are used to improve the power factor. In
fractional hp motors, they are used in the starting winding
to temporarily convert the motor into 2ph motor to make it
self starting
Is This Answer Correct ? | 28 Yes | 0 No |
Answer / gunasekaran
To improve the power factor of the motor. motor is inductive
load it draw reactive power from system.so we have
compensate the reactive power component from capacitor.for
single phase motor capacitor used for stating purpose
also.and single phase motor are low power factor motor
because due to large air gap B/W stator and rotor so it draw
more current from system.so capacitor are use in induction
motor
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / manish
To run the motor,stating torque and current needs to start
the motor and this capacitor work as residual magnetesim
for the motor at stating point.
Is This Answer Correct ? | 0 Yes | 0 No |
using n1*n2 which type transformer is made; where n1 is primary turn and n2 is secondery turn
In the formula : Knee point voltage = Burden X alf / class, Please inform what is alf? regards Shashidhar M.R.
what is power factor
How to determine the short circuit current for breakers and VCB.
what is the prosses for getting of 33kv licence (i have completed my engineering degree & working in 33kv substation for contract basis )????
In siemens S7-300 PLC, what is function and function block ? What is the difference between them ? When to use function and when to use function block ?
why generaotr rating is in kva and dc motor in kw?
True or false question. 1.The fuse provide phase and neutral 2.power loss in electrical circuit can take place in (resistance or inductance or capacitance). 3.two phase system each phase has separated by a phase difference of (90 or 180 or 270 or 45). 4.3 phase balanced star connected load neutral current shall be (line current or phase current or zero or unity)
On a 6 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 42 AH). What Shall be the current rating of DC MCB ?
0 Answers TNEB Tamil Nadu Electricity Board,
how electronic energy meter works?
Briefly describe your ideal job?
what is the voltage regulation for unity and zero power factor?