For a certain load i need 100kw load ,In that case what
rating mccb should i use?
Answers were Sorted based on User's Feedback
Answer / chintan patel
It can be different for DC , 1phase AC , 3 phase AC , systems,
Lets calculate for all ,
1 ) For DC ( you have not mentioned Voltage but considering 230 V )
100 kw means 100000 watt
formula for DC power p= vi
100000= 230xi
i=100000/230= 434 amp
we always use current rating of the mccb is 1.5 times of full load current so we can use 434x1.5= 652 amp.
( if system is not running on full load select 630 Amp MCCB, if its on full load select 800A )
2 ) For 1phase AC,
Power: P = V I cos phi ( cos phi is power factor is not known assume 0.8 )
100000 W = 230 x I x 0.8
I = 543 Amp
we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 543 Amp X 1.5 = 815 Amp
select 800 Amp MCCB
3)
If load is 3 phase AC ,
Power P = sqrt(3) x V x I x cos phi
100000 w = 1.73 x 415 x I x 0.8
I = 174
we always use current rating of the mccb is 1.5 times of
full load current.
mccb required 174 Amp X 1.5 = 261 Amp
( if system is not running on full load select 250 Amp MCCB,
if its on full load select 315 A )
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kalyan sharma
for 100 kw we will use 3 phase supply inplace of single
phase.
use formula p= 1.732 vi cosphi
100= 1.732*0.415*0.8*I
I = 174 amp
we always use current rating of the mccb is 1.5 times of
full load current so we can use 250 AMPs MCCB.3P/4P.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / rajat
for 100 kw means 100000watt
use formula p= vi
100000= 230xi
i=100000/230= 430 amp
we always use current rating of the mccb is 1.5 times of full load current so we can use 430x1.5= 645 amp
| Is This Answer Correct ? | 5 Yes | 4 No |
Answer / r g walia
for 100kw load required 630 amp mccb will be used.
| Is This Answer Correct ? | 2 Yes | 3 No |
What is the rating of your substation and what are the different types of substations?
what is meant by star/delta voltages as 440/220 in a 3 phase induction motor, and why it should be connected on STAR IN 3 PHASE SUPPLY
State The Difference Between Generator And Alternator?
What is FTA card? How it works?
what is the accaptable voltage between neutral to earth & How to reduse the resistance of earth in chemical earthing
what would happen if u assume to insulate all the overhead lines and no insulators....??do you think it to b an advantag or a disadvantage??justify.
what will happen if 11KV is given to 1.5 square mm cable connected with constant load of 10A ?what will be the condition of cable after injecting the voltage?
Explain thin film resistors and wire-wound resistors
need to make a report. Need to choose a 3phase induction motor. Load conditions motor will operate in : Maximum Load: 30 Kw Speed: 2950 rpm Ambient temp: 20 cent Supply voltage: 440V Frequency: 50Hz need to look for the safety factor when choosing the motor, went through catalouge found a few, but dont know how to choose the safety factor allowing an extra load something above 30 KW to avoid any harm.
Supose we have one 220v A.C fan.if we provide 220v D.C what will be happen?
how do u calculate CT rating for 10 mva transformer
why use generator Earthing/Graunding.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)