Answer / radha
this is called wet leg system,so you are telling range -600
to 0 means your drum distance between HP & LP 600 mm and HP
and LP legs both are filled with condensate(water)
continueosly but LP leg distance higher than the HP leg,so
LP side pressure will acting 600mmWC extra, compare with HP
leg pressure,so we have to eliminate that pressure LP
pressure 600mmWC
thats why -600mmWC = 4mA
0 mmWC = 20mA
Is This Answer Correct ? | 23 Yes | 7 No |
Answer / automatic
the negative value used for wet leg level transmitter that
means, you have the HP side filled with a reference liquid,
a initialy you should entre the pressure value of this side
in considiration that's why when we isolate the transmitter
from the vessel we never drain the HP leg
Is This Answer Correct ? | 15 Yes | 5 No |
Answer / mavdiyaamit@gmail.com
I allways -600 to 0 range is used because maximum vacuum pressure ranhe is -760 mmHg so not use in -900 to 0
Is This Answer Correct ? | 0 Yes | 9 No |
where are following valves are applicable to install. can any valve be installed any line. globe valve butterfly valve boll valve gate valve
What is difference between sensors and transducers?
Q- What are the application in which PNP transistor is preferred over NPN ?
Define magnetic flow meter and mass flow meter.
how can i calibrate a smart temperature transmitter used by druck 720 process calibrator?
diffrence b/w accuracy and precision?
how control valve works?
what is stroke check for field instument transmetter's & AOV's
what does the ratio 800-400-300-200/1-1-1-1-1 in the specification of current transformer indicates?
Why Differential pressure transmitter is located below the tappings points for steam & condensible vapor flow measurement application?
control modes
Which type of pressure can be measured by these elements?