Can we operate a DG Set in paralell with Transformer ?
Answers were Sorted based on User's Feedback
Answer / ekanadam naik
yes we ca operate dg set with transfer but voltage and
freqency must be matched, with help of PLC,
| Is This Answer Correct ? | 20 Yes | 3 No |
Answer / a. venkatesh
All the power source it may be transformer or Alternator
(DG-DC power generator).
For parellel operation synchronisation is important. I.E
Voltage level, frequency, phase angle should be equal for
the both sources.
For checking the synchronisation previously DARK LAMP
METHOD was used. Now a days special relays used for this
purpose. Relays MES 120(Schneider), 7UT relays in Siemens.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sangram
yes, we can Theoretically do it. we want to use aditional
relay and some equipments like Reversepower relay, DF/DT.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / meka sekhar
theoretically DG can be operated parallelly with
transformer as long as voltage, frequqncy, phase angle are
within limits. However, in industrial practice, only
momentarily paralleling will be done between DG &
transformer. Sometimes if they want to check loading of DG,
it can be paralled with transformer so that it will not
affect loads which are connected to bus.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sangram patil
Yes, called as synchronizsation of DG & EB of both. for
this parallel operation we want to concentrate on Voltage,
Frequency & Phase angle of both of equal.
and for Auto loading & Autobalancing we want to use
Woodward, C&S OR scnhider make relay.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ram
no dg set can not be connected with x-mer DG can not give
constant freq.
| Is This Answer Correct ? | 2 Yes | 9 No |
is any body explain me why return current in three phase power system is less then in a red, yellow, blue phases??? as we know Ir+Iy+Ib=In then why nutral wire has less then phase current????
what is the right method of laying cable tray if we are using EOT crane in shed, better is below or up
what is negative and zero impedance in 3 phase induction motor ??
excitation limit of an excitor
what is the frequency standard with tolerance level for India?
which gas is filled in CFL
why we are using R,Y,B colours for 3 Phase ?
working principle of AC Servo Motor with its construction
what happen if field of dc shunt motor opens? what is function of putting res. in parallel to one phase of 3 phase IM? the power supplied by 5A source in circuit is given by------Watt.
why we not using 230kv directly why we are stepping down and then stepping up
In 63kva LT Distribution Box Why the outgoing of 63A kit kat is connected to 200 A link disconnector? as the output of kit kat is only 63 A?
For backup batteries connection,which method is best? series or parallel ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)