When should I use earth leakage circuit breaker for incomer
and when should I use it for each feeder seperately?
Answer / mubeen
If your load is unbalance,or distrubting to different
panels you should use Earth leakage relay not ELCB.ELCB can
be used for branch circuit or any sperate panel such as for
light, power sockets etc.Earth leakage relay can be use to
trip the breaker on calculated current.
Is This Answer Correct ? | 1 Yes | 0 No |
As per standard, transformer body earthing and other Equipment earthing (Equipment earthing) did not connect. but in LT side termination we are doing metal glanding in both side Transformer to PCC Panel through armoured cable, now X'mer body earthing and PCC Pane earthing (Equipment earthing) both are connect.is this safe for X'mer or other equipment?