When should I use earth leakage circuit breaker for incomer
and when should I use it for each feeder seperately?

Answer Posted / mubeen

If your load is unbalance,or distrubting to different
panels you should use Earth leakage relay not ELCB.ELCB can
be used for branch circuit or any sperate panel such as for
light, power sockets etc.Earth leakage relay can be use to
trip the breaker on calculated current.

Is This Answer Correct ?    1 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Which of the following alternatives will be cheaper (1) A 100 h.p AC, 3-phase motor (2) Four motors of 25 h.p each (3) Five motors of 20 h.p each (4) 10 motors of 10 h.p each explain

2520


what is physical distance of isolator to VCB in 33/11kv sub stations

1700


What is oscillator circuit?

680


Why derating factor os applied on Cables?

1517


how to calculate slip ring induction motor stator and rotor currents??

1736






what is the use of expulsition protective gap in 11Kv line.

1686


Why water bubbles when D.C. Current is passed through it? Why not when A.C. Current is passed?

1674


What is the meaning of 40X8X2 busbar dimensions for carring load of 400 Amps

1578


What is speed mode?

1255


what is per unit calculation?looking for simple and strong explanation thk u

2440


what is the vvvf in the dumbwaiter?? or lift. what is the actual process?/

1620


1. The DC generaror,s induced output emf is connected with a DC motor(as load). when increasing the load of the motor by using brake drum or any way. what are the parameters will changes in both motor and generator(voltage, current, resistance, frequency, speed, torque, power, flux etc...) 2. Similarly for AC generator and AC motor 3. similarly if using DC batteries instead of DC generator, What happens?

1694


1.what is mean by 8/20 micro sec waveshape

1796


What is the difference between Encoder and Resolver?

2889


what is the role of energy meter in distribution system ?

673