For having nonavailablity of 10 Amps fuse, a lineman replace
the same with 5Amps two strand, Do he correct ?
Answers were Sorted based on User's Feedback
Answer / gravityguru
connecting them in series will not serve the purpose but
connecting them in parallel will serve our purpose..
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nagaraj pole
both are same rating but thing is only rating lable changed
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / santosh kawade
No.
If 10 amps fuse not available replce the same with 5 amps
two strand is not correct.
Because while connecting two strands in parallel current
distribution between them will not be equal and if one fuse
fail above 5 amps the other automatically fails
subsequently.
Santosh Kawade
9224 69 3116
Is This Answer Correct ? | 1 Yes | 4 No |
WHAT IS TANK CKT.?
we have a 2000kva step down transformer at our site. The HT side is charged from 22000V. So the primary current will be 52.48A. So why the HT breaker(SF6 ABB) is rated of 1250Amps ?
What is infinite Busbar?
what is the formula for computing cable tray size & capacity
A system having the charactristic eqation (s+1)(s+2)(s-3)=0 is (a)stable (b)unstable (c)marginally stable (d)critically stale
What is the formuala to calculate the rating of motor protection circuit breaker
why transformer rating is in KVA?
Does dry and oil transformers both require dedicated neutral, because in my project we are using 2500kv dry star delta transformer, where they say neutral not required and even it is not provided in our substation. can u let me know
What is mean by vector group? For what purposes we doing vector group test in transformers?
why in america the supply frequency is applied as 60 HZ. but in india we use 50 HZ.
1 Answers Elcom International, HCL, NTPC, OMC,
WHY IS THE UNITY POWER FACTOR NOT THE MOST CONOMICAL POWER FACTOR?
what is the difference between power transformer & distribution transformer and what are their ratings respectively?