why exterrnal C.T. protection is used even though ACB& VCB
is having inbuild C.T. protection?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
In-built protection is for currents exceeding the rated
current of the breaker,which is usually higher than that of
your requirement.Further, you can not alter this unless you
replace the cts.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / k.prakashchandra
In other words ,if the in-built CT does not meet your
requirements ,you have to use external ones.
Is This Answer Correct ? | 0 Yes | 1 No |
Which is stiffer between salient pole rotor and cylindrical rotor synchronous machines? Justify your answer.
How the Transformer oil testing is done & Why oil dielectric goes LOW & what is solution for that ??
how you will decide the distance between the power transformer and its fencing
In Designing the rating & accessories of a MCCB how to choose the type of releases..means what is the basis for selecting, thermal magnetic, electromagnetic & microprocessr based releases
why middle phase should used for earth fault and other phases used for over current in overcurrent and earth fault relay?
What is the use of starter in tube light fitting.how it works.
what is differant beetween overload current and phase current?
What happen if the 24 volt DC supply is disconnected from air circuit breake ?
why CERAMIC material is used in insulators??
why transformer does not obey ohms low?
directional relay is typically used to respond in fault condition who it can be used just as reverse power protection which purely senes direction reversal to operate a circuit breaker?
what is negative,positive abd zero sequence current explain clearly