How to use a insulation resistance tester on a three phase
electric motor?
Answers were Sorted based on User's Feedback
Answer / pswin
The purpose of insulation resistance tester is to test the condition of insulation. On three phase motors, we need to do the insulation test between winding to windings and windings to ground. Before the testing, we need to take out the connections(star or delta). Choose 500 V scale on meter and proceed to test.Full scale will be 100 Mega Ohm. Minimum will be 0.5 Mega Ohm and if lower than this result, motor cannot be used.
Is This Answer Correct ? | 10 Yes | 2 No |
Very simple. Measure ir between
r-y,y-b, b-r r-e,y-e,b-e
Is This Answer Correct ? | 0 Yes | 0 No |
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
how to synchronize 4 nos. of diesel generator sets of different capacity (kva)?
For 6600/433 distribution transformer we apply secondary side 433 volts how much voltage in primary side.
What shocks us , Current or voltage?
how a synchronous motor is used as a resistor,capacitor and an inductor?
why you don not show protection and type of isolation in key single line diagram?
What is the de rating factor of cable? What is the importance of the de rating factor in cable selection?
what happens to the supply voltage if there is any change in frequency?
Enlists the applications of sampled data systems?
I Have 3 Phase 10 KW AC Alternator i found one phase weak, so what will be the reason & what action shouls i take to rectify the same.
. Is there a simple method to measure the horsepower of a small motor (1-3 hp) for a non-technical person
What is reactance? what is the function in Auto transformer and why high leakage reactance?