How the earth fault relay works please explain?????????
Answers were Sorted based on User's Feedback
Answer / greenhat25
When a fault occurs, a current flows in th secondary winding
of th current transformer.
If th current is greater than th setting of th relay, th
electromagnet is energised and attracts th armature.
The action of th armature closes and opens th normally open
and close contacts respectively, thereby closing or opening
th trip circuit.
The shunt trip coil or UV trip coil is energised or
de-energised and th circuit breaker will trip.
Is This Answer Correct ? | 13 Yes | 6 No |
Answer / avd
In continuation to above answer, there are different
schemes to detect earth fault in the system
1. By using residual connections of three phases CTs
2. By using CBCT
3. By using a neutral CT at transformer neutral point.
Is This Answer Correct ? | 4 Yes | 2 No |
how to find out capacitor range?
what is the design factor that affects the size of a motor ?
different between horse power and break horse power
CFL lamp is what type of load?
what is mean by potential and potential free contacts
What is the basis for selecting Vk/2 or Vk/4 for REF and Differential protection of Transformer and What is the significance of magnetising current
why do we prefer -48 volt instead of -24volt or -12 volt etc. ??
What the formula for calculating no.of earthings & size of earth strip for 100mX90m shop.
surge tank, hrc fuse, earthing transformer, firm power objective type
why the manufacturer provide M and C terminals ? why they will not internally short them ?
What are the main faults of DC generators?
0 Answers Mercantile Marine Department,
how can we measure 220kv or more than these voltages ...?and also how can we conform whether we r getting 220kv from generating stations throuth the h v transmission lines?