WHAT IS THE MINIMUM IR VALUE FOR CABLE CHARGING
Answers were Sorted based on User's Feedback
Answer / pravin kumar
The minimum Insulation Resistance value for the power cables
2mega-ohm/kv this is both applicable for LT& HT side
for ex:
11 kv power cable need IR value is 22 mega-ohm
Is This Answer Correct ? | 25 Yes | 10 No |
Answer / pgr ram
for HT cables (6.6 KV to 33KV) above 500 megohms is
required. For LT cables (1100 volts) minimum 100 meg ohms
is required
Is This Answer Correct ? | 20 Yes | 13 No |
Answer / deepak marya
IT IS ONE MEGA-OHM PER KVA AT 70 DEGREE CENTIGRADE.IR VALUE
IS HALF FOR TEN DEGREE CENTIGRADE RISE IN TEMP.
Is This Answer Correct ? | 4 Yes | 4 No |
How to caluculate number of batteries to connect a three phase ups by KVA?
What is the possible cause for failure of lightning arrestors in outdoor substation under normal condition
what is the use of cable in our environment ?
what is the difference between on line UPS & INVERTOR
how can found motors folt current ? how can disided circuit breakers caoicity and breaking capicity ?
dear friends plz send link about reluctance & universal motor .thank u
what are the standard values for resistances(Megger testing) between L&N, L&E and N&E (L=Live,N=Neutral, E=Earth)?
what effect will 10 milliampere current cause to human body ???
A low wet bulb temperature indicates
circuit breaker work alone during fault condition or need any relays ?
tan delta test of current transformer.
why dc is used in control circuit for mv & hv switchgear instead of ac