WHEN I AM CONNECTIN TWO ELCB IN PARALLEL.ONE ELCB
TRIPPED...HOW IT HAPPEND??
Answers were Sorted based on User's Feedback
Answer / vinod
When two ELCB in prallel sending current & return current
of each ELCB will not be equal (example one ELCB is
sending 4 amps to the load but due parallel the retun
current from the load to the same ELCB may not be 4 amps,
retun path through other ELCB treat as a earth fault, so
one ELCB will trip.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / karthick
pls to be check elcb current rating in case rating are
different. lower rating elcb got easily tripped. in case
elcb rating are same connecting load to be check
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prashant
if loae is high then you connect two cb, if any one of cb
is trip then ohter cb is also trip. Due to high current.
because if any cb is trip then all current is flow through
the second cb.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / arvind
when you are connecting two ELCB parallel then its mean the
voltage between these will be same but not the current, so
which ever ELCB is connected to higher current side is
getting trip if the current is flowing greater than the set
value.
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / purushotham
the ELCB's are connected in parllel, so the voltage in the
ckt is equal but current is diff. so if one coil trips the
ckt will works on second ELCB and total loading depends on
that second ELCB.
| Is This Answer Correct ? | 0 Yes | 0 No |
which type of motor is suitable for water suction pump ?
why ct ,cvt should be stored in a vertical position?
how we can improve power factor from 0.8 to 0.85 or 0.9 & how we identify its either lag or lead ? thank you
How eddy current generation support the idea of train braking?
how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)
why any Elelctricity board insist not to change the buren of their metering CTs or PTs for metering purpose? as a example elect. board not accepted that any customer change their metering CT or PT core burden from 5VA to 15VA.. why?
what is the use of starter in tube light?and what it contains
12 Answers L&T, RRB,
Is CBCT protect human life? If yes than how?
How to calculate the current capacity of the 3C / 1C Al/Cu power cable???
How to calculate ant test the burden of Current transformer
testing of transformer
What is the meaning of EDO in DG panels?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)