WHEN I AM CONNECTIN TWO ELCB IN PARALLEL.ONE ELCB
TRIPPED...HOW IT HAPPEND??
Answers were Sorted based on User's Feedback
Answer / vinod
When two ELCB in prallel sending current & return current
of each ELCB will not be equal (example one ELCB is
sending 4 amps to the load but due parallel the retun
current from the load to the same ELCB may not be 4 amps,
retun path through other ELCB treat as a earth fault, so
one ELCB will trip.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / karthick
pls to be check elcb current rating in case rating are
different. lower rating elcb got easily tripped. in case
elcb rating are same connecting load to be check
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prashant
if loae is high then you connect two cb, if any one of cb
is trip then ohter cb is also trip. Due to high current.
because if any cb is trip then all current is flow through
the second cb.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / arvind
when you are connecting two ELCB parallel then its mean the
voltage between these will be same but not the current, so
which ever ELCB is connected to higher current side is
getting trip if the current is flowing greater than the set
value.
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / purushotham
the ELCB's are connected in parllel, so the voltage in the
ckt is equal but current is diff. so if one coil trips the
ckt will works on second ELCB and total loading depends on
that second ELCB.
Is This Answer Correct ? | 0 Yes | 0 No |
What are the types of class b amplifier?
Why more than 2.5 MVA distribution transformers (secondary is 440V)are not used in india.
why is the conservator tank painted white on the transformer
what is raw power & normal power
star delta starter single line digram
Which device of PlC does share load between DG sets when DG are running in perallel?
why do we put a transformer on soak before loading it
how can calculate static 3phase 4wire CT & PT operated energy meter constant when calibrating using refference meter suppose we have 11kv/110v PT and 30/5A CT, the meter constant is 160imp/kwh, where meter is showing MW energy? give me solution which constant i feed in my refference meter for calibration of energy meter?
Can anyone tell me some hints about what type of questions are asked by the interviewer by an Electronics engineer when company is installing an IPP and wants a team of engineers?
why steady state stability limit is greater than transient stability limit ? How it can be explained ?
Why the brushes used in dc machines are made of carbon not from other metal?
What are the reasons for AVR failure in LT DGsets ?