for measuring current and etc.,why we use value of 1.732 in
three phase calculation. not in single phase.why

Answers were Sorted based on User's Feedback



for measuring current and etc.,why we use value of 1.732 in three phase calculation. not in single..

Answer / thowsif_emerson

The power in watts is equal to volts times amps, but
we must use "phase" volts and "phase" amps to calculate
power.
Calculating these phase relationships requires a little bit
of
trigonometry.

In a "Y" connected circuit, the voltage measured line to
line is not the
true "phase" voltage [phase to neutral voltage], but the
combination of
two voltages that are out of phase by 120 degrees.

Assuming a balanced load, the current in any of the three
phases is the
same as that measured in each line because the line will be
attached to
one end of the phase so there cannot be any difference. We
need the

phase voltage times the phase current to get the phase
power.

There are two phases connected between each pair of lines
in a "Y"
circuit, and since the voltages are not in phase, they do
not add together
to make the line voltage twice the phase voltage. It turns
out through
some basic trigonometry, that the line voltage is equal to
each of the two
phase voltages times the sine of 120 degrees, and the sine
of 120 degrees
is "one-half" the square root of 3. Adding those two halves
together
gives the LINE voltage as the square root of 3 times the
phase voltage.
Or conversely the phase voltage is the line voltage DIVIDED
by the square
root of 3.

So the power in any phase, assuming, again, a balanced load
is
the line voltage times the line current divided by the
square root of 3.

For the three phases, then, the total power is three times
the power in
any phase. 3 X the line voltage X the line current divided
by the square
root of 3. 3 divided by the square root of 3 simplifies to
just the
square root of 3. Multiplying that, as you noted, by the
power factor
converts volt-amps to watts assuming the power factor is
other than one.

In a delta connected circuit, the same problem exists
except with the current measurement. Here, the line to line
voltage
measurement is the phase voltage, but the line current is
composed of two
currents that are out of phase by 120 degrees, and you
guessed it, the
"vector sum" of the two phase current components is the
square root of
three times the current in any phase. And, the phase
current is the line
current divided by the square root of 3, so the power
equation works
exactly the same for both the "Y" and the Delta connected
circuits.

Is This Answer Correct ?    46 Yes 6 No

for measuring current and etc.,why we use value of 1.732 in three phase calculation. not in single..

Answer / prathap

in single phase system power P=V*I*COS(pi)where
V=voltage,I=curent,but in 3 phase system P=root(3)V*I*COS
(pi),(root(3)=1.743)

Is This Answer Correct ?    5 Yes 3 No

for measuring current and etc.,why we use value of 1.732 in three phase calculation. not in single..

Answer / shashidhara

It is just a coincidence of mathematics and vector algebra!!!!!

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

What is the lower limit of megger value for 66/11KV power Transformer ?

7 Answers   MSETCL Maharashtra State Electricity Transmission Co Ltd, Torrent Power,


what is the max load on a 10 mva transformer & plz define it with its formula

0 Answers  


1)how many types of earth? 2)how many types of megger and how to select that range? how much time taken for megger calibration( we r using megger)

1 Answers  


how does the switching of capacitors in a capacitor bank take place when we use them at the load side to reduce the power factor?

2 Answers  


What is the Different Between Breaker and One and half breaker.

2 Answers  






What is the universal motor?

0 Answers  


in three 3.5 core aluminium ug cable. one cable is used for one phase by shrting R,Y and B wires and other 2 cables used for Y and b phases. balace 3 neutral wires are made common and connected to load. suddenly neutral current was more than line current what is the reason behind this?

1 Answers   DLF,


why voltage swells and dips in transmission line?

2 Answers  


What do you mean by linear and bilateral network?

20 Answers   Automation, Disa, EGCB, Infosys, OPTCL, TICT,


What is electrical grounding?

0 Answers  


How can we get a Neutral from a three phase suply? If we meet all three phases at a point to take neutral then why dont thay get sparked?

1 Answers  


what is the function of an auto reclosure relay in OHL?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)