Answer / paul
I am not aware of Class 10A, I am aware of Class 5, 10, 15,
20, 25 & 30. These refer to the tripping curve of a
thermal/electronic relay - eg Class 10 means 6 x motor full
load current (FLC) for 10 seconds (normal squirrel cage
induction motor). Therefore Class 30 means 6 x FLC for 30
seconds and Class 5 means 6 x FLC for 5 seconds etc....
Is This Answer Correct ? | 19 Yes | 1 No |
Answer / amit
10 A means tripping class of relay..like10,20,30 A
Is This Answer Correct ? | 11 Yes | 3 No |
Answer / jayant jain
Class 10A relays are those that will trip within 2 to 10
seconds when supplied with 7.2 times the current setting.
Similarly there are Class 10, 20 & 30 relays where the
tripping times at 7.2 times the current varies. The class is
helpful in correct selection of the relay for your motor
protection as it takes into account the heavy start or
normal start of your motor.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / jitendra gosai
Standard tripping classes are 10 A, 10, 20, 30. The
tripping
class indicates according to IEC 60947-4-1 the maximum
tripping time in seconds under specified conditions of test
at
7.2 times the setting current and specifics tripping and non
tripping times for 1.5 and 7.2 times the setting current.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / jothiswaran.s
Adding to Mr Paul , the class of relay indicated the error
percent. usually matched with the CT. also they will not be
marked as "class 10A"
Is This Answer Correct ? | 0 Yes | 3 No |
in conventional fan regulators how the current varies with speed?
briefly explain the main blocks found in a microprocessor based system
why are we using multiples of 11 in substation.
What is mean by Sensitive Earth fault & what are the effects
What Normal(Tangent) towers and Tension(Cut-point) Towers?
1 Answers ABB, BGR Energy, NTPC, Powermec,
difference between isolater and circuit breaker?
what happens if power factor is maintained at 0.9?give me the answer in technicall way rather than telling the penality n all
How to do stting of vl250 siemens MCCB
What is resistance reading of earth copper rod with grid and without grid?
How we can make sure cable size of LT cable without any parameter.
2 Answers Paradip Port, Siemens,
IS RTCC AND OLTC REQUIRED FOR 500 KVA 11KV/433V TRANSFORMER FOR AN INDUSTRY?
7 Answers IGCAR, TNEB Tamil Nadu Electricity Board,
WHAT MEANT BY MCC PANEL?