in thermal overload relay class 10A indicate what

Answer Posted / paul

I am not aware of Class 10A, I am aware of Class 5, 10, 15,
20, 25 & 30. These refer to the tripping curve of a
thermal/electronic relay - eg Class 10 means 6 x motor full
load current (FLC) for 10 seconds (normal squirrel cage
induction motor). Therefore Class 30 means 6 x FLC for 30
seconds and Class 5 means 6 x FLC for 5 seconds etc....

Is This Answer Correct ?    19 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

A 100 kVA , 400 v/250 kv testing transformer has 8% leakage reactance and resistance on 100 KVA base . A cable has to be tested at 500 kv using the above transformer as a resonant transformer at 50 hz . if the charging current of the cable at 500 kv is 0.4 A find the series inductance required . Assume 2% resistance for the inductor to be used and the connecting leads . Neglect dielectric loss of hte cable . what will be the input voltage to the transformer ?

4488


Why we are using Isolation Power Transformer inplace of commercial power transformer? What's the difference between them?

1529


What are the relays in ACB and VCB

1697


i am in need of AC SYNCHRONUS MOTOR 30KW. ANY ONE KNOWS THE MANUFACTURER OF SAME. ALSO MOSFET AC CONVERTER 20KVA CONT.OUTPUT.

1472


CBCT selection

1798






why wire sizes are 3/29 or 7/29 and why not wire sizes are 2/29 or 6/29?

4661


how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size

1902


how to conduct dc resistance test for rotor of an alternator and how to measure the rotor dc resistance value theoritically?

2821


How to find out damper winding failure for synchronous machine?

999


Why in ESP Positive earthed

2568


Y phase plates are used in transmission line??? what is there need???

2438


What is the difference between the relay and the circuit breaker?

613


how can we design robots

1459


1.what is difference between ATS & STS main use. 2.what is difference between ACB& VCB With symobles,and main partes, manimum range. 3.How many types of relays and main function.

5609


Why PT voltages are measured with respect to ground? What do u mean by voltage or current polarized.

1926