cascade controller is feed back or feed forward or both
Answers were Sorted based on User's Feedback
Answer / rajkumar
its a feed back loop.
Cascade Control uses the output of the primary controller
to manipulate the setpoint of the secondary controller as if
it were the final control element.
Reasons for cascade control:
* Allow faster secondary controller to handle
disturbances in the secondary loop.
* Allow secondary controller to handle non-linear valve
and other final control element problems.
* Allow operator to directly control secondary loop
during certain modes of operation (such as startup).
Requirements for cascade control:
* Secondary loop process dynamics must be at least four
times as fast as primary loop process dynamics.
* Secondary loop must have influence over the primary loop.
* Secondary loop must be measured and controllable.
Reasons not to use cascade:
* Cost of measurement of secondary variable (assuming it
is not measured for other reasons).
* Additional complexity.
| Is This Answer Correct ? | 18 Yes | 2 No |
Answer / arun/instrumentation design en
cascade controller is a feed forward controller
cascaded controllers takes feed from the primary
controller, and manipulates the feed as feed to the
secondary controller.
cascade controllers means itself two or more controllers
cascaded in series to make process control faster and
precise..
| Is This Answer Correct ? | 1 Yes | 11 No |
Answer / nagarajan
cascade controller is the feed forward which is controlling
the process .
| Is This Answer Correct ? | 5 Yes | 16 No |
What is the difference between mmwc and mmwg?
If fire would be inside the plant which fire detector is to detected the fire.
What's the Installtion procedure of DP Transmitter for Gas,steam and water?
how we convert Mili ampere to temp txt,level txt,flow txt,pressure txt range value
How can we calibrate the level interface for Fisher® FIELDVUE® DLC3000?if use water to calibrate and our liquid SG are 0.75 and 1 ,Displacer height=14" and How much should be set SG in trasmitter during calibrate,for URV and LRV how shold be set
Tr. Wiring for calibration.
HELLO FRENDS ,, I M IN THE MIDST OF TROUBLE .. JUST LITTLE HELP ME... SUPPOSE ,, I HAVE A CLOSE VESSELE TANK ( HEXANE MEDIA ) ,, I M USING ROSEMOUNT 2051 DPT FOR LEVEL APPLICATION .. ITS CALIBRATE RANGE IS.. . 0 TO 950 MMH20 ..I DID CALIBRATED DPT WITHOUT REMOVING IMPULSE LINE OF HIGH AND LOW TAPPING.. & WITHOUT DISTURB 3 WAY MANIFOLD..!!! BUT ,,, DURING CALIBRATION I SELECT RANGE BY HART LRV IS 900 MMH20 & URV IS 1300 MMH20 ,, BUT ,TANK LEVEL SOMETIMES 100 % AT 1100 MMH20 , SOMETIMES 1300 MMH20 ..IN THIS CONDITION .. WHOLE LOOP FAILED ,, MAIN THING IS THAT ,, HOW TO CUSTOME RANGE SELECT ?? AND IF I USED RANGE OVER THE ORIGINAL CALIBRATE RANGE ,,,THEN WHAT ERROR WILL BE COME ??? HOW TO ZERO CALIBRATION OF DPT... HOW TO ZERO TRIM BY MANIFOLD ?? AND FOR TANK LEVEL PURPOSE ... WHICH UNIT I CAN USE ??? IS THERE ANY CALCULATION OR CALIBRATION .. IF YEH .. THEN PLZ JUST GIVE ME CALIBRATION STEPS FOR DPT.. THANKS YOURSSSSSSS
how many parts of valve positioner?
How do you identify an orifice in the pipeline?
Whether the DP transmitter can be utilised in the medium of Vaccum for the measurement of Level?
Determine the manipulated variable, controlled variable, and the measured variable given a description of various typical industrial processes.
what is thermopile?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)