How can we calibrate the level interface for Fisher®
FIELDVUE® DLC3000?if use water to calibrate and our liquid
SG are 0.75 and 1 ,Displacer height=14" and How much should
be set SG in trasmitter during calibrate,for URV and LRV
how shold be set
Answer / iit
Calculation # If the calibrating liquid is water:
In the DLC3000 (Need Hart to communicate)
-ON Basic set up_PV set up set PV is Level
-ON Basic set up_PV set up set Specific Gravity =1
-ON Basic set up_PV set up_PV Rang set URV=14"and LRV=0".
1. First close both the primary isolation valves and drain
the liquid inside the chamber.
2. Fill water up to the center of lower flange level =0"
=0%
2.1 At DLC3000 on Basi set up_Sensor calibrate_Two Liquid
Lvl cal select Lower cal to get 0" =0% output
3. Fill it up to the center of the top flange level =14"
=100%
3.1 At DLC3000 on Basi set up_Sensor calibrate_Two Liquid
Lvl Cal select Upper cal to get 14" =100% output.
4. Fill it up to 50 %, check linearity.
After calibration completed with water and back on service
for interface
On DLC3000
-ON Basic set up_PV set up set PV is Interface
-ON Basic set up_PV set up set upper SG is 0.75,Lower SH=1.0
-ON Basic set up_PV set up_PV Rang set URV=14"and LRV=0".
and close drain valve and open both the primary isolation
valves unit ready to in service
Is This Answer Correct ? | 8 Yes | 5 No |
why we use 0.2 to 1.0 kg/cm2 output in control valve
what r all the type of viberation measurement measuring in turbin? what's the output of viberation sensor?
two common seiling liquid used in seal pots are:
what is the zero elevation and zero supresstion in level measurement, how can use it?
difference between vaccum and draft
Punj lloyd is coming in our Jadavpur Universtiy campus for campus placement. Please send me some hints about the writtend exam. My email id is subratafriends@gmail.com
0 Answers IGL, Punj Lloyd Ltd, Shapoorji Pallonji Group(SPCL),
what is the PID controller?
How can we measure the level of a closed system like drum
How to get Cv of control valve having following parameter ,i.e inlet pressure 4.5kg/cm2 outlet pressure 1 kg/cm2 specific gravity 0.808
How a oxygen sensor & analyzer work at boiler or furnace, what’s the principle & science is beyond this, How O2 sensor scene & convert signal & move toward analyzer & analyzer show reading in percent?
1 Answers GS Engineering Construction, KNIC,
how many parts of valve positioner?
In electronic board one fuse(rating 230v,100ma)showing 2.5 ohms with multimeter,then the fuse is healthy or not.