how much Amp we can put in 1200kva generator?
Answers were Sorted based on User's Feedback
Answer / vipinkshishodia@gmail.com
Hi All this is Shishodia & i am a new user of this site .
Well, following formula can be used to determine the amps
from KVA.
I= P(W)/(1.732 X VOLT X Power Factor)
I=KVA X 800/(1.732 X 440 X.8) Note 1 KVA = 800 Watt
So,
I= KVA X 800/(1.732 X 440 X 0.8)
100 % - 1574.63 Amps
80 % - 1259.71 Amps
So always put in Amps 80% mean 1259Amps for 1200 KVA
generator
Is This Answer Correct ? | 3 Yes | 6 No |
Why is a plain induction motor unsuitable for wide speed control?
I AM A ELECTRICAL PANEL BOARD DESIGN ENGINEER.IF I GO ANY INTERVIEW ,TECHNICALLY WHAT ARE QUESTIONS I WILL FACE FROM INTERVIEWER?
Will any motor burn if voltage provided is lesser than the rated voltage???? If yes, then how is speed control possible with voltage control
it is difficult to interrupt a capacitive current because (a)it has a leading power factor (b)current magnitude is very small (c)the restriking voltage can be high (d)stored energy in the capacitor is high
2 Answers DGVCL Dakshin Gujarat Vij Company, MGVCL, UGVCL Uttar Gujarat Vij Company Ltd,
Calculation for the adequacy of 380 KVA neutral earth flat size
The electrical energy required to raise the tempreture of a given amount water is 200 kwh. If the heat losses are 20%, the energy required is?
How many energy meters can be connected on a 15VA Voltage transformer. please send a calculation sheet.
what should be the resistance valve of healthy earth pit
can we synchronize star system generators with delta system transmission line ? and how ?
Why is a synchronous motor always star connected??
0 Answers Bhushan Power Steel,
what is mcb
what is ground clearence in transmission system.is it varies wit conductor size,height of poles,span.