At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC
54A as per the nameplate. At the time of starting it draws
840A instead of 390A (7.2%). As per the data sheet also its
390A starting current. it thru a dol starter from the MCC.
can anyone tell what is the problem in the motor
Answers were Sorted based on User's Feedback
Answer / ranjan prasad
From the question motor terminal connection is not known.
However this problem may arise if you will connect the
motor in delta instead of star. First check the terminal
connection of motor, if it is in star, connect in the same
manner.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / kannapa
do not use dol starer above 2.2kw rated motors
use star to delta starter it can withstand.
check also connections.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / r.v.giribabu
First Check the healthyness of the motor.
1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.
Follow above steps adn yoiu will identify the problem.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / wani y.s.
First Check the healthyness of the motor -
1. Check the winding resistence
2. Check insulation resistance using megger.
3. Check the bearing and apply the lubricant as applicable.
4. Check the healthyness of connected load.( It should not
locked etc.)
5. If all above is OK. Then remove the motor from load &
ensure it is starting in ideal condition.( Hope connections
you are following up as given on the nameplate)
If it is starting in no load that means load GD squre is
high. Motor is taking longer time to start.You have to
select proper heavy duty DOL starter to withstand the
longer starting time. But ensure that motor is having
thermal time capacity to withstand this time.
7. You can also go for VFD as a starter this will definetly
will solve your problem no need to take care of thermal
time of the motor. Only select proper VFD to suit starting
torque of your application.
Is This Answer Correct ? | 0 Yes | 1 No |
pl. check motors connection in terminal box if it is
connected in star then current may increased.
Is This Answer Correct ? | 5 Yes | 13 No |
how to calclate fault level
Why the underground cables will Punchar? or what is the reason to burst the underground cables?
what is mean Boost voltage and what is working principle of Tube light
What was the Dg set radiator and lube oil temperatures trip in ACB
why we use post insulators in no ofstacks at substation for supporting equipment ? why we not use single post insulator
is dc transformer is possible ?
Whats the minimum value for I.R. that can be allowed for HT & LT alternators for operation?
how to set the transformer differential relay
what are the things that can cause a three phase motor to crawl?
what is the current law ?
Is it legal of using 3 phase motors in 2 phase in Tamilnadu?
write a program that prints prime numbers from 1-20 in digonal form