what is NGR in generator?
Answers were Sorted based on User's Feedback
Answer / siddu
NGR Means Neutral Grounding Resistor, used for higher
rating of transformer because to allow the heavy fault
current through it, during the fault so -----NGR resistane
value so less Ex. 9.5 Ohms
low resistance allow the fault current easily
Is This Answer Correct ? | 24 Yes | 5 No |
Answer / raviteja nowduru
NGR stands for neutral grounding resistor.it connected
between neutral point and ground.it is a type of grounding
to limit the current not to eliminate fault currents.
Is This Answer Correct ? | 8 Yes | 1 No |
Answer / meka sekhar
NGR means neutral grounding resistors normally connected in
neutral circuit of transformer & generator to limit the
earth fault current. After installing NGR in neutral
circuit, earth fault current will be in the range of few
amps i.e. 5A t0 300 A.
Is This Answer Correct ? | 2 Yes | 0 No |
What is the meaning of 40X8X2 busbar dimensions for carring load of 400 Amps
why solinoid coil used in tripping rely?and why not other type coil?
how to test a motor from megger
what is the working principle of energy saver control panel. please give the complete calculation & theory.
what is difference between ac voltage and ac current
Advantages/Disadvantages of earthing of neutral bus on MSB instead of separate neutral earthing for transformer/DG sets feeding to MSB
if we convert kva into Ampers,which one formula use by us,pls tell me?
The armature of shunt dc motor has 0.8ohm resistance and motor is to run on 120V circuit.If motor is suddenly thrown on circuit while armature at standstill then current drawn by motor will be??Also back emf in normal running is 110V
DEAR SIR/MADAM,CLEARLY EXPLAIN ABOUT CRAWLING AND COGGING EFFECTS IN INDUCTION MOTOR.
I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila
what is the unit of electricity????????????
why occ curve is not tracing back when we are bringing rheostat back in reverse direction?