We have 2 no. 4MW DG set. and GEB supply.
But, we running, only 1 DG set. when we done APFC/Power
factor setting : 0.90, then winding temp. Low. but when
setting done : 0.83, then Winding temp. increase.
WHY Why ? ? ?, plz give me answer.
Answers were Sorted based on User's Feedback
Answer / suthan prabhu
The reacive power taken by the load will be same but the
current supplied by the source will increase bcoz the p.f
is decreased from 0.9 to 0.83.hence the winding temperature
increased.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / gurucharan singh
this is clear that at lower pf settings, its the DG which
compensate for the KVAR. which results in the high winding
temperature. For this check the plant loads connected. And
KVAR supplied by EB & DG. Also during parallel with grid DG
generally act as KVAR compensator along with KW supplied.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / rajnikant dodiya
Simple,
power factor increse, current decrese ane hence losses
(I^2R) reduces. But if Power factor reduces, losses
increases with square of current which makes dg to be hot
compared to increase pf.
Is This Answer Correct ? | 0 Yes | 0 No |
Can 33kva/415v transformer be run underground? If the answer is yes why and if the answer is no why?
Explain the operation of variable frequency transformer?
Explain principle of Soft-starter & how its working???
What is the equivalent circuit of a transformer and its vector diagram?
Does the direction of rotation of d.c. Shunt motor would get reversed if the armature current and field current both are reversed?
in cable joints procedure what electrical problems have been solved out ?
MICOM P122 OC/EF RELAY HAVE HARMONIC RESTRAIN OR NOT?
What is VCB'S @ ACB'S.Plz explain Briefly
when we decide to use soft starter drive or vfd drive in mcc to operate apump?
Explain how you intend to work under pressure to meet up with deadline target?
In the ACB breaker capacity is 2000Amp but this each phase taken 1250 But total beldibg load is 600amp or 700amp watt is the problem
why capacitor using the induction motor?