wat is syncronization . wat parameter will take for
syncronization.
Answers were Sorted based on User's Feedback
when one Generator is running and suppose its rating is
1500 kva/1200 kw,and load increased and we wants to put
more load on GENERATOR . So then we have to run second
generator and to be shift some load on second generator,
otherwise the generator will be over loaded and tripped on
over-load fault. when we connect two generators parrallel,
this arrangement is called synchronisation.we connect the
out-put supply of both generators parallel by
synchronisation.In synchronisation we have to match these
parameters--phase sequence, frequency and voltage.when all
three parameters match we ON the breaker and
synchronisation complete and now we can put more load
(about 2000 kw) on generator.
| Is This Answer Correct ? | 17 Yes | 1 No |
sychronisation is important when parrallel operation of two
generators or when we connect a generator to grid.
The generator supply must only be connected to a live
grid,
1. Phase angle difference
2. Voltage differnece
3. frequency diffenrence (slip)
between the generator and grid voltage are within
permissible limits and the phase sequence of both generator
and grid rotating field should be identical.
| Is This Answer Correct ? | 3 Yes | 2 No |
what is the easiest method of short circuit current calculation ? pls. derive with a mathematical example in real life application.
how make to Incident and accident report
which connection is there in a rotor of the motor
2 Answers All Trades Electrical, HAL,
Wat is power factor exact meaning in terms of technical terms plz explain ?
What is EOL?
Installation method of self treated earth electrode.
How to test transformer
Difference Between Differential Relay and Restricted Earth Fault Relay of Power Transformers
how to protect motor in dol starter having capacity of 30 hp.40 hp?
which transfofrmer oil break down voltage strength get will be more if oil sample taken from bottom of tank or oil sample taken from top of the transfomer tank.
What is bode plot?
If any HVDC line is going with positive & negative(the negative usually have return path of current with earthing electrode). Now the question is if this HVDC earthed electrode which is using as return path and earthed any nearby 400kv or 220kv AC substation equipments. which will be the impact of this on AC substation & its equipment, how severe may be this and what should be the minimum distance require between HVDC earthed electrode and AC substation equipments? It's really an high engineering level question...Dare to answer and increase your knowledge.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)