Answer / ccic
Cable/wire , i.e. the conductor should be rated for at
least 125% of the FLA. The upstream CB protecting this
conductor should also be rated similarly, i.e. for a load
with 100A as FLA, the cable should be able to carry at
least 125 A. The cable derating factors (type of cable,
type of installation, ambient condicions, Voltage Drop etc)
should then be used to select the ACTUAL cable. The CB
should be rated for 125 A (Instantaneous Trip setting)
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / k.p.sharma
Size depends on two things
1. Current rating normally load current should be 70-80% of
cable's minimum capacity.
2. Voltage drop should be within limit i.e. for lighting 3%
and for motor during starting within 10%.
Is This Answer Correct ? | 4 Yes | 9 No |
please send previous exams question papers
Without seeing the nameplate descriptions of a rotating machine,Is it possible to say which one is a motor and which one is a generator? How would you certain this?
what is the diffrance between earthing and grounding...?
bus bar design conditions and sizing pls tell me quickly
Form fator is the ratio of?
Detailed working of a diesel generator set ?
1 Answers Airtel, Honda, Kirloskar,
Why do we apply both Differential and REF (HV and LV) protection schemes on YNyn configuration of a transformer?
what will happen when reverse reactive power occurs in alternators?
why there is spacing between two rails in railway?
as a electrical student why should i hire you?
why is the conservator tank painted white on the transformer
1600kva capacity Transformers how the bucholz relay,Oil temperature,winding,surge relay relays setting are to be done