WHAT ARE THE DATAS REQUIRED FOR SCS SIGNAL LIST PREPARATION?
It depends on your SUB STATION CONTROL SYSTEM (SCS)
supplier and client, and load despatching authority SCADA
system.
Generally Load despatching authority demand:
I) Remote control -on-off control oF CB,STATUS OF
INDICATION,PROTECTION AL+TRIP SIGNALS ,FEED BACK SIGNAL.
OLTC COUNTER,
2) INDICATION - A,V,F,PF, MW,MVAR,
3) METERING IN -OUT MWH,MVARH,
4) sTATUS OF ALL CB,DS,ES, PLC,
5) MAIN BUS ,INCOMMING,OUT GOING.
6)SUB STATION dc VOLTAGE, UPS ALARM
7)FAULT LOGGER REPEATITION SIGNAL.
THIS IS A VERY EXPENSIVE TASK. SCS SUPPLIER MUST FINALIZE
CLEARLY,AFTER FINALIZING SIGNAL SUCH ,AS DI,DO,AI,AO ,LOGIC
SEQUENCES, SHALL PROCEED HIS WORK.
tARIFF METERS ARE VERY EXPENSIVE. SCS MUST FOLLOW LOAD
DESPATCHING REGULATION AND ITS SPECIFICATION.
| Is This Answer Correct ? | 1 Yes | 0 No |
how to i get B licence,i am completed BE electircal and electronics engineering.i want to konw the proceduure to get b licence
how give earthing to shif and aeroplane which is away from earth?
I am going to appear for the RRB Chennai junior Engineer online exam. Please send me the previous exams question papers (also solved) to my mail id: rrkhandhar@yahoo.com
we have 3*1 MW generator one NGR is common for all it will be selected during paralle our problem is two generator ca be paralled but when slecting third one we need to close NGR selection on third one other wise voltage not matching why?
what is the working of hydrent system.
What is the limitation of kirchoffs law?
Can Anyone Answer anyone of these ? Q1) why direct SOLUTION of Load Flow Studies in Not Possile ? Q2)Why majority of Buses in power system are load buses Q3)Why one of the buses in Power system is taken as reference bus (slack or swing) Bus ? Q4)Bus Admittance Matrix is a sparce (means it contains some zero elements ) matrix , give reason
what is legal process of dg set?
why are use corona ring in high tension line switchgear?
What is effect on in zone and out zone fault if CT chosen for phase side is Vk/2<5mA and Neutral side is Vk/2<15mA on REF protection of Transformer
Which loss in DC machine is maximum?
in india,we use 230V,50 Hz,whereas many other countries use 110V,60Hz.what r d advs and disadvantages of each of them?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)