Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


when the operation engineer told you that he gives the
control valve order to open but there is no response !
what will you do ?
and if you found that there is astuck , what will you do ?
(note : it is apanumatic valve )

Answers were Sorted based on User's Feedback



when the operation engineer told you that he gives the control valve order to open but there is no..

Answer / chitturi bhaskara rao

1.First measure 4-20mA in field side if cannot get 4-20
then check AO card , if u got 4-20 in field side then check
positioner ,
2. make sure thatt sufficent air supply i,e 3 to 4 bar at
inlet of positinoer.
3.If all correct still valve nvr moves then remove
positionner from the valve and supply the air directly to
actuator ( to 4 bar max) then valve moves smoothly then
check angle of postioner while ur fixing positoner on
control valve .
4 if valve nvr moves smoothly means in side valve jam need
to send over haul

Is This Answer Correct ?    20 Yes 0 No

when the operation engineer told you that he gives the control valve order to open but there is no..

Answer / maneesh

after doing all the priliminary inspection if u found the
valve is struck, u can directly give the air supply to the
actuator not:direct applying og air supply may diamage the
valve it should be done with sufficiant care.if the struck
is minor by repeaded giving of supply air will slowly
remove the struck.agfer this still its struck u can remove
the valve from the praocess line and chel the valve body
whether any solid material bloks the way.if that u can
clean and fix it back

Is This Answer Correct ?    2 Yes 0 No

when the operation engineer told you that he gives the control valve order to open but there is no..

Answer / b.kumaran

after doing all the priliminary inspection if u found the
valve is struck, u can directly give the air supply to the
actuator in a repeated manner.if the struck
is minor by repeaded giving of supply air will slowly
remove the struck.still its struck then loosen the body
bolts and try to open by the above method. If still there is
a struck up then u can remove the valve from the process
line, dismantle and clean the valve body whether any solid
material bloks the way.

Is This Answer Correct ?    0 Yes 0 No

when the operation engineer told you that he gives the control valve order to open but there is no..

Answer / 808

Simulate 4-20mA it with a DMM at control valve. If it works
there, then check wiring.

Is This Answer Correct ?    1 Yes 3 No

when the operation engineer told you that he gives the control valve order to open but there is no..

Answer / aatif alvi

check if the proper volatage i.e 4-20ma is changing the the
operation engineer changes he valve position. if it is
changing the the problems might be with the solonoid..some
times moving the solinoid with screw driver makes it work
again,, as it got stuck due to rusting.

Is This Answer Correct ?    1 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

applications of 1-5v and 4-20ma?

4 Answers  


how to calculate the total flow in square root

0 Answers   PTI, Qatar Kentz,


on which principle control valve works?

3 Answers   Lupin, Reliance,


How to calibrate smoke Dectector

0 Answers   KOC,


Pressure transmitter working Principles?

1 Answers  


in a power plant which system are compensated?

2 Answers  


Flow tax range 0 to 100 mmh2o ,flow rate 40 tons /hr, I want change flow rate example 42 tons/hr so tx range ?

2 Answers  


can anybody tel me how a vfd or any field instrument communicates/interface with plc/scada/cs.

0 Answers   Honeywell,


Why drum level range is given -500 to 0 mmwc pls give me that answer

1 Answers  


1 How to calculate dp transmitter steam and water? 2 impulse line for liquid steam and gas

1 Answers   Sitara Chemical Industries,


We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.

1 Answers   Shyam Steel,


whats the working of principal thermocouple

6 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)